    Goodman GMPN locking out
    I recently purchased a house with a propane GMPN060 installed. It works fine on either AC or fan modes but when on heat it will lock out. Specifically the inducer motor starts, the HSI energizes, the burner will ignite but shortly extinguish. Unit retries 3 times and shuts down. Being a logical kind of guy, I tried cleaned the flame sensor and when that failed, I replaced it to no avail. I have no idea when the furnace was last run. The house sat empty for nearly a year. Propane guy adjusted the regulator to 11" when he installed the tank.

    Looking for ideas... comments or suggestions.
    O
    Ozhoo's Avatar
    Ozhoo Posts: 4, Reputation: 1
    New Member
     
    #2

    Oct 23, 2009, 06:06 AM
    Just measured the FS current. It starts around 2 uA and goes as high as 5uA before the burner shuts down.

    O
    Ozhoo's Avatar
    Ozhoo Posts: 4, Reputation: 1
    New Member
     
    #3

    Oct 23, 2009, 06:17 AM
    Quote Originally Posted by Ozhoo View Post
    Just measured the FS current. It starts out around 2 uA and goes as high as 5uA before the burner shuts down.

    O

    Well, call me crazy but that 5uA seemed a bit high, so I randomly dialed back the propane regulator 3 turns and would you believe, she runs like a champ.

    O

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Exhaust pipe on Goodman GMPN furnace. [ 1 Answers ]

Hi all. I'm trying to find out if the connection, for the exhausting vent pipe, should be glued where it connects to the drain trap assembly that is connected to the combustion air blower? I have placed a link below, to the manual, so you can see the area in question. Look on page 22 (Drain...

Goodman Model gmpn series heats then just stops [ 3 Answers ]

My unit will kick on and heat and then it will just stop working. Indicater light on board shows solid red as if everything is normal. Any Ideas?

Goodman GMPN won't fire [ 3 Answers ]

Trying it for the first time this year, unit is 9 years old. The furnace blower keeps running but there's no fire and after a few minutes it cuts off. LED is solid. Could the ignition switch be shot? Thanks.