    How to wire a electric fan heater with an inline thermostat at the end
    I have an electric fan forced air heater at 2000 watts powered by 240 volt wiring, hot/hot. I have a 12/2 wire that comes from power and connects to it, it works great and no problem. I want to add a 5/2 programmable in line thermostat. Is there a way to do that, without running power to the thermostat first, then running it to the heater, again, this is an inline 240 volt rated thermostat from Honeywell, and the supply already goes to the heater itself. I don't want to (if possible) have to rewire it so it goes to the thermostat first, but rather have it run to it second, i.e.. Put the thermostat at the endo fot he line. I tried to do this, and it powers fine, but is still controlled by the onboard thermostat switch on the heater. So I am doing something wrong. Can anyone help? Thanks!
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Oct 20, 2009, 06:52 PM

    In ANY case the thermostat has to be (electrically) ahead of the heat that it controls. You will need a 12-2 from the panel to the tstat and another 12-2 back to the heat.

    Assuming there is enough room to junction all those wires inside the wireing cavity of your heater, you could run two 12-2 cables from the heater to the thermostat. The first one would connect to the line from the electric panel with NO connection to any part of the heat except for the grounding (bare or green) conductor. The other end of that first cable would go to the input or LINE terminals of the thermostat. The second 12-2 would come back from the LOAD terminals of the thermostat and would connect to the heat strip. Most likely you would eliminate the existing thermostat mounted in the heating unit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do you wire an electric hot water heater ? [ 4 Answers ]

How do you wire an electric hot water heater ?

How do I wire up a Marley electric baseboard heater? [ 2 Answers ]

This is my first post, so thanks in advance for any help. I'm finishing my basement & am installing a pair of Marley electric baseboard heaters in parallel. I've got the basics done: double 20 amp breaker, 12ga wire, Double line break thermostat. Here's the issue: The units will accept left or...

Is a 30 amp breaker + #10 wire good for this electric heater [ 8 Answers ]

Hi, I am about to purchase and install this ceiling mounted electric heater: Fahrenheat Ceiling-Mount Automatic 5000 Watt Electric Heater, Model# FUH5-4 | Heaters | Northern Tool + Equipment It uses 240 Volts, 5000 Watts at 17,065 BTU/hr. It seems that it needs a 30 amp breaker and #10...

I have a ten wire General Electric thermostat [ 4 Answers ]

I am trying to replace 10 wire thermostat with 5 wire thermostat. Do not know how to connect

What size wire for electric heater? [ 2 Answers ]

I'm hoping someone can help with this question. We are installing an electric wall furnace, 240 volt, 38 amp, 9.2kwh. I was told by the guy at the hardware store to use size 8 wire. The instructions (?? ) that come with the unit don't sat anywhere what size is to be used! Is size 8 wire correct?...


View more questions Search