    Entrance wire zise
    Hi, I need to run about 1300 feet of wire to a little house in the country, out side the usa so there is no inspection, some people use 10 or 8 gauge
    Wire but can't use noting that takes allot of current.
    I would like to use a microwave, 110v window ac & a 110v tankless water heater wich usses about 25 amp and not having to turn of averyting else. But price matters so I am thinking aluminum wire but was wondering what is the smaaler gauge I can use I don't have anyting else the draws allot of current. I don't mine having a 35 to 55 amps box if it will work. Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 18, 2009, 04:41 AM
    1300 feet is a ridiculous distance to run 120 volts, so get the largest aluminum wire you can afford, and deal with whatever voltage drop you get.

    I get you need #500 MCM Al to deliver 35 amps @ 120 volts 1300 feet for a 5% voltage drop.

    So I get that would be too costly for you.

    Since most electrical appliances, motors, etc will run on plus or minus 10% voltage range, a #4/0 Al would be the smallest for 35 amps. Anything smaller the Vd will be too high to allow the appliances to run at all.

    All we know here is how to do things properly, under reasonable conditions, so to expect proper results.

    For this run at minimal costs, your guess is good as anyone's.
    ldenito's Avatar
    ldenito Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 25, 2009, 11:33 AM
    Thanks, would a dry transformer work how much kva would I need
    Sorry for the questions I don't know anyting about electricity just trying to see how to save $ I am only going to use the cabin 2 time a year.
    Any other help is apreciated. Thanks dennis

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Using Al. Wire for service entrance wire. [ 5 Answers ]

Was looking for help, failed elt. Service inspection due to the use of al. wire coming from the outside disconnect to the main panel inside the house. Wire is proper size but was informed that 2005 nec required use of copper?

Size of Service Entrance Wire [ 0 Answers ]

Hello I will be installing a new electrical service. It will be a 5 ganged meter socket running 4 apartment panels and 1 landlord panel. Each apartment will have a draw of between 60-67amps and will be on 100Amp panels. The landlord panel will draw between 56-62 amps and will also be on a 100...

Service entrance wire size [ 1 Answers ]

What size wire is required for a 200 Amp service panel?

Service entrance wire size. [ 8 Answers ]

I am in Honduras, where, the NEC does not apply, and what a mess we have without it.. I can put any size wire anywhere, and no one cares, except me. I am putting in a 150 Amp Service and the breaker panel will be about 50 Ft from the Meter.. I have not yet figured the size wire I need to the...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search