    Older model lennox switch setting
    I have an older model lennox furnace and would like to know hwt the limit switch should be ste at to keep the blower from running too lon. The model number is G1203-110-6 it I removed the plate and itd set at 105 and 200 and the blower runs until the thermostat reads 78 and the stat is set at 75 and the stat is only 3 months old
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 16, 2009, 04:23 AM
    The thermostat in the auto mode does not cause the furnace blower to operate. The control on the furnace you found controls the blower motor in the heat and auto fan mode. The 200 degree setting is probably a limit safety setting and should not be disturbed if it is so. The other setting could be moved a bit higher or lower to accommodate you. Some thermostats also have a setting for the heat anticipator and on many thermostats this is adjustable. Follow the directions that came with your thermostat to adjust the anticipator. You might be better off adjusting the thermostat anticipator first since it might have more to do with your problem than the fan and limit control.
    markhil37's Avatar
    markhil37 Posts: 16, Reputation: 1
    New Member
     
    #3

    Oct 16, 2009, 12:28 PM
    Thank you I will try that when I get home. Ill look at my thermostat and see if there's an adjustment I can make

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wireing diagram for Lennox model: CB29M-41-1P [ 1 Answers ]

Hello, I recently purchased a Lennox Elite Series Furnace/Heat Pump used and I need to wire the unit in. Does anyone out there have a wireing diagram for this unit?? Thanks, Larry Denney

Wiring for older lennox furnace [ 2 Answers ]

I have an older Lennox furnace that had some wires melted in a flash fire. Does anyone know where I might get the wiring schematics to rewire the unit? When I went to move the wires they broke apart and know I want to ensure that they are connected properly again. The model is G8R-120-1, serial...

Wiring diagram for a Lennox Model E8-25-1 Electric Furnace. [ 1 Answers ]

The wiring Diagarm on the front panel is not clear enough to read. Also I need to know the proper sequencers & limits to use in this furnace. The furnace has been worked on by several people and I would like to rewire With all new parts


View more questions Search