    Old Westinghouse Circuit Breaker Data Needed:
    While conducting an arc flash study, I found the following supply breaker on a panel that is 35-40 years old. Westinghouse type QNBRL2100 (quicklag); it is 100amp, 240vac, 2 pole. I am looking for the AIC rating and whether it is thermal magnetic, but can not find it listed in the usual sites that sell used bkrs. Any leads on how to find this information?
    Thanks
    Newton1Law's Avatar
    Newton1Law Posts: 60, Reputation: 5
    Junior Member
     
    #2

    Oct 18, 2009, 04:33 PM
    I am not familiar with this particular circuit breaker but you may find it listed on the side of the circuit breaker. You will have to remove it from service most likely. Baring that effort, circuit breakers were usually manufactured to certain minimums of AIC. For instance most of today's circuit breakers come with a minimum rating of 10,000 amps AIC. Over 35 years ago, I believe some of the 5,000 amp AIC units were still being used.

    As far as to it operating thermally, magnetically or both, usually at the 100 amp level they worked thermally for overload protection and magnetically for fault protection but like you I was not able to find data on that CB unless it was replaced by the Cutler-Hammer BR series of circuit breaker.

    Hope this is of some help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Oct 19, 2009, 06:06 AM

    I would use 10 KAIC for this device, as it most likely the rating of the unit. You could go back and look for the label. The arc flash energy for a 100 amp at 240 volts is not that hgh as it stands. NFAP 70E calls for Category 1 at the most for this level.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Circuit Breaker trips because two bathrooms and master bedroom on same circuit [ 6 Answers ]

Some electrician committed a blunder in my opinion about 17 years ago. The master bedroom and two full bathrooms are all on the same circuit. If two hair dryers are used at the same time, it will trip the breaker every time. In figuring out what amperage would be required for two hair dryers and...

Circuit breaker trip after install of GFCI breaker [ 3 Answers ]

I'm replacing an outlet under kitchen sink that garbage disposer and dish washer were plugged into because they stopped working. The old outlet was not GFCI. So I'm attempting to replace it with one. Our home was built in the '50s and has no ground line yet. I used an extension cord to plug them...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Replacing Circuit Breaker with Higher AMP Breaker [ 8 Answers ]

Excuse me, I did look at the code book as is suggested in your Sticky. The NFPA may answer this question, but I am not knowledgeable enough to recognize it: Our offices are upstairs in an older (renovated home) building with modern wiring. We have 4 computers, 3 printers, and miscellaneous with...


View more questions Search