Water Pressure Issues - Inground Well
Hello -
I don't have very many details, since I don't know where to start. We live in South Carolina, and our home is just one story. We have a well with a pump, the water pressure inside the house is very strange. When you turn on the water in the house/tub, it may trickle for up to 4-5 minutes, and then we will get a blast of full pressure, then it will start to slow down again. This issue has been going on for months now.
In the garage we have a tank, which I guess is some type of water filtration system to pull out the sand in the water, not sure if that helps.
I really don't know where to start.
Also, I have a Sprinkler System, which we don't use, and it does have a couple small leaks that I know of. I have been wanting to disable the Sprinkler system to see if there is some underground leak, but I don't really even know what to do or where to start.
Any ideas ? I can provide more details hopefully if you have specific questions.
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 13, 2009, 04:47 PM
|
|
What kind of well do you have? Is the pump in the garage or is it at the bottom of the well? Does the tank have a pressure gauge on it or close by? Is there something on the top of the tank that look like a tire valve stem? Do all of your valves act this way of just the tub?
|
|
 |
Junior Member
|
|
Oct 13, 2009, 05:08 PM
|
|
 Originally Posted by hkstroud
What kind of well do you have? Is the pump in the garage or is it at the bottom of the well? Does the tank have a pressure gauge on it or close by? Is there some thing on the top of the tank that look like a tire valve stem? Do all of your valves act this way of just the tub?
What kind of well do you have ? I don't really know, the pump is out in the yard, I am guessing at the bottom of the well, the pump/pipes are under one of those fake rock enclosures in the yard.
In the side room in the garage, is where the water comes into a pre-charged air tank, the water leaves there and goes through a sand filter, and then into the hot water heater.
Yes, there is a tire valve stem in the garage coming from the ACE Precharged Water System Tank (That's is what is on the Tank). I don't see any pressure gauge on it, or close by.
All valves act this way in the whole house. My very weak diagram shows the water path, this is what is in the garage... Pre-charged Tank to inline Sand Filter, to Water Heater.
Tank ____ sand _
Tank | |
Tank | |
Tank _____| |_______waterheater
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 13, 2009, 05:58 PM
|
|
Should have ask, does this happen with both hot and cold?
When is the last time you flushed the sand trap tank?
When is the last time you flushed the water heater?
Press the air valve on the pressure tank for a few seconds, do you get air or do you get water?
Go to the well head, a pressure gauge should be there as well as the pressure switch. Have some one open a faucet, watch what happens to the pressure gauge.
I don't really follow you schematic. Save the picture below to you computer. Open with Paint. Use cut, copy, and paste to move things around.
|
|
 |
Junior Member
|
|
Oct 13, 2009, 06:48 PM
|
|
 Originally Posted by hkstroud
Should have ask, does this happen with both hot and cold?
When is the last time you flushed the sand trap tank?
When is the last time you flushed the water heater?
Press the air valve on the pressure tank for a few seconds, do you get air or do you get water?
Go to the well head, a pressure gauge should be there as well as the pressure switch. Have some one open a faucet, watch what happens to the pressure gauge.
I don't really follow you schematic. Save the picture below to you computer. Open with Paint. Use cut, copy, and paste to move things around.
Happens Hot and Cold
Sand Trap Tank - The whole plastic housing was changed out this past weekend due to a crack in the housing, right now it's clean, no sand, new filter.
Water Heater - Water Heater is less than six months old, have not flushed it yet.
At the well head, I don't see any pressure gauge. I did just find a pressure gage near the pressure tank in the garage room, it's reading between 20/30. I think the switch is also there?
When I just opened a faucet the pressrue gauge did not move, and the water is trickling out. About 4-5 minutes later, the pressure picks up (Just noting same behavior)
I have just taken some digital photos of the outside well head, and the equipment inside for you to have a better look.
I just uploaded a few digital photos of the situation for your review. Let me know if you can see them or I can email them to you. I could only upload 3 this time.
Thanks for your continued help.
 Originally Posted by Network_Admin
Happens Hot and Cold
Sand Trap Tank - The whole plastic housing was changed out this past weekend due to a crack in the housing, right now it's clean, no sand, new filter.
Water Heater - Water Heater is less than six months old, have not flushed it yet.
At the well head, I don't see any pressure gauge. I did just find a pressure gage near the pressure tank in the garage room, it's reading between 20/30. I think the switch is also there ??
When I just opened a faucet the pressrue gauge did not move, and the water is trickling out. About 4-5 minutes later, the pressure picks up (Just noting same behavior)
I have just taken some digital photos of the outside well head, and the equipment inside for you to have a better look.
I just uploaded a few digital photos of the situation for your review. Let me know if you can see them or I can email them to you. I could only upload 3 this time.
Thanks for your continued help.
To add - Pressing air valve on pressure tank brings air not water
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 13, 2009, 07:23 PM
|
|
I don't see a sand trap tank. I only see a pressure (really a bladder tank) , a filter and a water heater. That thing next to the pressure gauge is the well pressure switch.
Am I understanding correctly that as the flow at the faucet changed there was no change in the pressure gauge?
|
|
 |
Junior Member
|
|
Oct 13, 2009, 07:37 PM
|
|
 Originally Posted by hkstroud
I don't see a sand trap tank. I only see a pressure (really a bladder tank) , a filter and a water heater. That thing next to the pressure gauge is the well pressure switch.
Am I understanding correctly that as the flow at the faucet changed there was no change in the pressure gauge?
Correct, I just got down on my hands and knees, looked directly at the pressure gage, and had the wife turn on the kitchen sink faucet, the gage did not move a bit. Still sitting in the middle between 20/30
BTW - The cover on the pressure switch says it's a SquareD PumpTrol
Sorry to mislead you on the sand trap tank, I was referencing the filter, since it does catch sand.
Sometimes this happens - Turn on the faucet (Any) trickle for 3-5 minutes, then the water stops completely, then full pressure blast, then it starts to slow again.
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 13, 2009, 08:49 PM
|
|
You either have a blockage or the pump and tank are not set up properly.
First blockage. The blockage has to be between the pump and the water heater since you experience the lack of volume on both the hot and cold. The only things between the pump and the water heater are the tank, the filter and two ball valves. I take it that you replace the clear plastic cover on the filter only , not the complete filter. I know that because of the rust on the old galvanized fittings. What is the red button on the filter?
One or both valves could be blocked but they are ball valves and not easily blocked. The remaining thing is the tank. It could have the bottom filled with sand if you have a lot of sand in your water.
The other thing is the proper set up of the tank. Twenty to 30 lbs is awfully low. Right now I don't know if that is the cut on or cut off pressure. Usual pressure settings are a 20 lb spread, usually cut on at 30 and cut off at 50 or cut on at 40 and cut off at 60.
First things first. Open a faucet, watch and listen to the switch. When the points close (the pump comes on) note the pressure. Close the faucet. When the points open (pump turns off) note the pressure gauge again. Also note how long it took to reach cut off pressure.
Turn off the breakers to the pump. Drain the entire system. Check the air pressure in the tank with a tire gauge. Adjust tank pressure to 30lbs. Adjust switch cut on pressure, that should be the short screw, to where points are just closed. Tightening should increase, loosening should decrease setting. Reduce tank pressure to 28 lbs.
Turn breakers on. Let pump run and adjust cut off pressure, should be tall screw, so that pump turns off at 50 lbs. Also note time.
Remember this time that electrical connections are live.
|
|
 |
Uber Member
|
|
Oct 14, 2009, 03:43 AM
|
|
Net, have you tried bypassing the filter?
|
|
 |
Eternal Plumber
|
|
Oct 14, 2009, 06:40 AM
|
|
The first thing I would do is increase the pressure at the control box. I would increase it to 50 PSI cut off pressure. If you need instructions on how to do this click on back. Is there a check valve any where up on top? It sounds like you have a submersible pump with a faulty foot valve that's allowing the water to drain back down from the surface. The delay happens when the water has to be drawn up from below. I would install a check valve and see if that doesn't stop the delay. Good luck, Tom
|
|
 |
Junior Member
|
|
Oct 14, 2009, 06:53 AM
|
|
 Originally Posted by speedball1
The first thing I would do is increase the pressure at the control box. I would increase it to 50 PSI cut off pressure. If you need instructions on how to do this click on back. Is there a check valve any where up on top? It sounds like you have a submersible pump with a faulty foot valve that's allowing the water to drain back down from the surface. The delay happens when the water has to be drawn up from below. I would install a check valve and see if that doesn't stop the delay. Good luck, Tom
I guess I will be having to call a plumber ? I don't have the skill set to install a check valve, or even know what it is. How do I find a plumber that works well wells ?
How do you increase the pressure at the control switch, by turning the screw down ? I have done that, I have turned the short screw down 2 turns and the behavior is not getting any better. Pressure in the bladder tank is 15.5 with tire gauge. (I clicked back but did not get anywhere)
I have another pressure control switch that I can swap out, it's a Square D pumptrol. Do you think this could help at all, someone suggested the pressure control switch may be bad. What do you think.
Thanks
|
|
 |
Junior Member
|
|
Oct 14, 2009, 06:58 AM
|
|
 Originally Posted by hkstroud
You either have a blockage or the pump and tank are not set up properly.
First blockage. The blockage has to be between the pump and the water heater since you experience the lack of volume on both the hot and cold. The only things between the pump and the water heater are the tank, the filter and two ball valves. I take it that you replace the clear plastic cover on the filter only , not the complete filter. I know that because of the rust on the old galvanized fittings. What is the red button on the filter?
One or both valves could be blocked but they are ball valves and not easily blocked. The remaining thing is the tank. It could have the bottom filled with sand if you have a lot of sand in your water.
The other thing is the proper set up of the tank. Twenty to 30 lbs is awfully low. Right now I don't know if that is the cut on or cut off pressure. Usual pressure settings are a 20 lb spread, usually cut on at 30 and cut off at 50 or cut on at 40 and cut off at 60.
First things first. Open a faucet, watch and listen to the switch. When the points close (the pump comes on) note the pressure. Close the faucet. When the points open (pump turns off) note the pressure gauge again. Also note how long it took to reach cut off pressure.
Turn off the breakers to the pump. Drain the entire system. Check the air pressure in the tank with a tire gauge. Adjust tank pressure to 30lbs. Adjust switch cut on pressure, that should be the short screw, to where points are just closed. Tightening should increase, loosening should decrease setting. Reduce tank pressure to 28 lbs.
Turn breakers on. Let pump run and adjust cut off pressure, should be tall screw, so that pump turns off at 50 lbs. Also note time.
Remember this time that electrical connections are live.
That part in the picture you can see is the spicket to let the water out of the bladder tank. When I open a faucet the pressure is between 20/30, when the pump finally cuts on, the pressure does not change on the gauge, it's always the same. I have yet to drain the bladder tank, I need a hose end to put on it, don't have it right now. Current pressure in bladder tank is 15.5 with digital gauge. I tried to pump it up with a pump that plugs into the cigarette lighter for the car, but it would not increase, I guess there is no need to try and get any more air in the tank if I have not drained it yet ? I wonder if a portable air tank would work for that.
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 14, 2009, 06:59 AM
|
|
If you have only 15 lbs of tank pressure I think you have found your problem. Go through the set up procedure as described. Not necessary to drain entire system. Turn both valves off. Turn pump breakers off. Connect hose to tank drain. Empty tank of all water. Pressurize tank with drain valve open. You can use a portable air tank if you don't have a compressor . You can even pump it up with a bicycle pump but it will take a while. Portable air tank may take more than one tank of air. Watch pressure gauge, it may be defective.
|
|
 |
Eternal Plumber
|
|
Oct 14, 2009, 07:03 AM
|
|
First turn off the power at the breaker box, then pull the cover off the pressure switch and you will see two spring loaded bolts secured with nylon nuts,(see image) One tall, one short. To increase the pressure, turn the nut on the tall bolt down. This will increase both the cut in and the cut out points. If you just want to increase the cut out pressure without increasing the cut in point then turn the nut on the short bolt down. Good luck, Tom
|
|
 |
Junior Member
|
|
Oct 14, 2009, 01:09 PM
|
|
 Originally Posted by hkstroud
If you have only 15 lbs of tank pressure I think you have found your problem. Go through the set up procedure as described. Not necessary to drain entire system. Turn both valves off. Turn pump breakers off. Connect hose to tank drain. Empty tank of all water. Pressurize tank with drain valve open. You can use a portable air tank if you don't have a compressor . You can even pump it up with a bicycle pump but it will take a while. Portable air tank may take more than one tank of air. Watch pressure gauge, it may be defective.
So far so good, I completed the steps, and so far it's working again. I will update tomorrow after it makes a full day. Thanks a bunch for all of your help.
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 14, 2009, 03:07 PM
|
|
Good. Give us an update tomorrow. Next thing you are going to do is put a stop valve on the sprinkler system. I agree with Tom that you are probably losing pressure back down the well line. But since you seem to suspect a leak in the sprinkler, I think that is where its is rather than the pump foot valve.
|
|
 |
Junior Member
|
|
Oct 14, 2009, 03:18 PM
|
|
 Originally Posted by hkstroud
Good. Give us an update tomorrow. Next thing you are going to do is put a stop valve on the sprinkler system. I agree with Tom that you are probably losing pressure back down the well line. But since you seem to suspect a leak in the sprinkler, I think that is where its is rather than the pump foot valve.
I want to completely disable the sprinkler system, when you go back and reference the picture of my pump head earlier in the posting, is the pipe that has a T in it where they spliced in to run the sprinkler system? Could I not completely seal it off right there. I don't have a clue where any of the solenoids are in the yard. Some things you just don't think about looking into when buying a house...
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 14, 2009, 05:16 PM
|
|
Yes, you can cut pipe as shown and cap. Cap both pipes. You can also install a PVC stop valve. Just need a valve, a coupling and a short length of pipe. Have to dig around lower pipe so it can move up and down about 1". Use the blue Wet or Dry PVC glue so you can turn pump back on immediately after.
|
|
 |
Junior Member
|
|
Oct 14, 2009, 07:15 PM
|
|
 Originally Posted by hkstroud
Yes, you can cut pipe as shown and cap. Cap both pipes. You can also install a PVC stop valve. Just need a valve, a coupling and a short length of pipe. Have to dig around lower pipe so it can move up and down about 1". Use the blue Wet or Dry PVC glue so you can turn pump back on immediately after.
Thanks again. I think I understand, but I don't under stand what you mean about "dig around lower pipe so it can move up and down about 1"
I understand the two options, but I don't understand about the pipe and it even being able to move ?
Thanks !
|
|
 |
Home Improvement & Construction Expert
|
|
Oct 14, 2009, 10:27 PM
|
|
Pipes fit inside of fittings. In order to get the last piece in you have to be able to move one or the other up or down to get it in. How would you get the valve of the attached sketch, in the line if you couldn't move either pipe up or down?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Water pressure issues (not the ussual)
[ 4 Answers ]
I have a funny situation in the town I just moved to. Instead of having 3/4" or 1" pipe bringing water into my house I have 5/8" pipe bringing in water. Because of this, when I run the shower (or some other item) there is not enough water pressure to run other taps, etc. There is the regular...
Well water pressure issues
[ 7 Answers ]
I have lived in my house for 5 years and have always suffered from low water pressure but just recently decided to investigate. Turns out the system never gets any higher than about 32 PSI. If I turn the pressure switch up, the pump just runs continuously and the pressure does not go any higher. ...
Mainly low water pressure, but also a couple other issues
[ 25 Answers ]
Hello
My wife and I purchased our house 4 years ago and have always had really good water pressure, up till about a month ago when it started to gradually decrease. This past weekend, I spoke with my dad about it and he said that the pressure tank could be water logged (I have well water). ...
Hot Water Pressure Issues
[ 6 Answers ]
I'm having a problem where the how water is sputtering out of faucets and making a loud "jerking" noise from the hot water tank area when the washer tries to pull in hot water. I tried releasing the pressure relief valve on the hot water tank which hadn't been done in a while but did not seem to do...