    Need proper size wire for subpanel installation
    I am an electronics technician & computer geek so I understand basic electricity but am not an electrician. I want to run 52-feet of wire from main panel to subpanel off a 60-amp circuit breaker inside of PVC conduit. I have run 3/4-, 1- and 1-1/2-inch conduit. What is the safest and most energy efficient giage of wire to use?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Oct 12, 2009, 11:03 AM
    First question, have you sized the load for this subpanel to make sure that 60 amp will meet your needs?

    Are you bringing 240 or 120 VAC or both to the panel.

    You would use a # "6/3" <corrected typo> AWG cable for 240/120 VAC.

    Stan: Thanks for the catching my typo.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Oct 12, 2009, 11:53 AM
    For a 60A sub-feed you would need at least #6cu.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Oct 12, 2009, 02:45 PM

    Conduit. THWN 4 insulated conductors. Wire is usually dual rated THHN/THWN. Conduit buried so the top is 18" underground. For non-conduit 24".

    I'm assuming a 240/120 sub-panel.

    Ground rod is required for detached structure.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Wire Size 60A Subpanel [ 1 Answers ]

I am finishing up a bathroom addition and need to add a subpanel next to the existing 200A main panel to clean-up several 'doubled-up circuits I found in the main panel as well as provide breakers for the new bathroom installation. I plan to install a 100A sub-panel within a foot of the...

Wire size selction for a subpanel [ 1 Answers ]

A family member has built a small (12X20') home shop for welding projects. A subpanel fed from the 225A home breaker panel will be used to feed a subpanel in the shop. Installed, the subpanel feed wire will entail a total run of circa 110 feet. Query: What is the correct size wire for this...


View more questions Search