    awgn70's Avatar
    awgn70 Posts: 2, Reputation: 1
    New Member
     
    #1

    Oct 9, 2009, 01:45 PM
    Can a double-pole thermostat replace a single-pole one?
    Hello -- this is potentially a dumb question, but I have a 1970's era house w/ 240v baseboard heat controlled with single-pole (copper) thermostats. I have a Honeywell TL8230A programmable thermostat which expects a double-pole box. Is there any way I can make this work? I've combined "control" and "load" wires and the digital control activates, and there's even a relay "click" on and off as I adjust the temperature setting, but no power gets to the baseboard element. Seems tantalizingly close, but perhaps I simply bought the wrong thing.

    BTW, I'm being very careful to cut power before I do anything... :-)
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Oct 9, 2009, 05:02 PM
    That thermostat requires 208-240 volt to operate. Your old thermostat was beaking only one leg of the circuit, leaving the other hot leg connected where the new thermostat breaks both legs of the circuit. Are both legs available in the box? You need both legs to the thermostat for it to operate properly.
    awgn70's Avatar
    awgn70 Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 9, 2009, 07:57 PM
    Ah, the other leg is not present inside the box but I can check to see if it runs behind the box -- we'll see and I'll post what I find.

    If this doesn't work, I believe that the RLV430 would work with a two-wire config? That's what the Honeywell tech help guy told me. (dang, I'll have to eat the $60 on this TL8230A, I guess)
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Oct 9, 2009, 08:51 PM

    The programmable stats actually draw their power through the heater element. That's how come they don't require batteries and it's also why you need two poles.

    Usually 240 volt stats are two pole except they function in a weird way. One pole is an on/off switch and it's on for all but the OFF position. The other pole is thermally switched by a bi-metalic piece of metal.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring single pole thermostat in double pole fixture [ 3 Answers ]

Hello, I am trying to install a line voltage programmable thermostat into a manual thermostat fixture. The programmable thermostat is Honeywell RLV430. Instruction manual here: http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf The...

From double pole to single pole thermostat -2 extra leads [ 3 Answers ]

The double pole thermostat for the baseboard heater has a red and a black wire coming in (from the circuit panel) and a red and a black going to the heater. The new single pole only has a red LINE lead and a black LOAD lead. If I attach red to red and then black to black, I have black (from...

Single Pole or Double Pole CB's at main using 12/3? [ 5 Answers ]

House is in CA, built in 1974 using the MWBC setup. From Main: 1) Has four single pole circuit breakers. 2) Four Hot running into house. 3) Two Neutral running into house. A) Circuit #2 handles part of Kitchen as well as bedrooms 1 and 2:

Thermostat - changing single pole to double pole [ 4 Answers ]

I am changing two thermostats on electric baseboard heaters from single pole to double pole so I can turn them off without flipping the breaker. The heaters are on the same dedicated circuit. The 1st box has 3 white wires wired together and 2 black. It did not matter how I wired the double pole...

Double pole or single pole thermostat for baseboard heater [ 2 Answers ]

A more specific question here: My 240v baseboard heater says it can be wired with a single or double pole thermostat. Since 240v is already "dual pole" with two hots, do I want to stick with a double pole thermostat? Are there advantages/disadvantages to each? Thanks.


View more questions Search