Control wire questions
I had a minor accident with my old thermostat so I'm having to replace it, I ran into a small problem though while tracing my wires back. On my thermostat, I have Rc/Rh which are jumpered together, and a W Y G. I understand all of that and how the thermostat works, but my problem comes at the other end, on the unit. It's a Heil NUGE100BG01.
I have W Y R G C on my unit, everything was working fine before, but the Y wasn't plugged up. That really threw me off because I assumed that Y on the unit would be AC compressor too.
Thanks in advance,
Chris Webb
Electrician
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 08:23 PM
|
|
There should be a two wire from the furnace to the outdoor unit, one wire should be connected to the "C" terminal and the other should be tied to the yellow wire. Doesn't have to be on the circuit board.
|
|
 |
New Member
|
|
Oct 8, 2009, 08:30 PM
|
|
 Originally Posted by hvacservicetech_07
the other should be tied to the yellow wire. Doesnt have to be on the circut board.
The yellow is on the G terminal at the unit. Should it be on the Y at the Thermostat?
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 08:35 PM
|
|
What color wire was on the G terminal at the thermostat? They should match unless they have been spliced elsewhere.
|
|
 |
New Member
|
|
Oct 8, 2009, 08:39 PM
|
|
It's yellow now.
I knocked the old thermostat completely off with a dresser I was moving, the wires were totally off the old one.
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 08:40 PM
|
|
Ok, what color and how many wires do you have at the thermostat?
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 08:41 PM
|
|
This is what it should look like...
R-24volt RED WIRE
W-HEAT... White wire
G-Blower... Green wire
Y-Yellow wire... A/C
|
|
 |
New Member
|
|
Oct 8, 2009, 08:47 PM
|
|
W= red wire
Y= no wire
R = green wire
G= yellow wire
C = black wire
Those wires are in a cable assembly and run straight from the unit to the Thermostat, no splices.
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 08:50 PM
|
|
Do you have air conditioning installed on this system?
|
|
 |
New Member
|
|
Oct 8, 2009, 09:04 PM
|
|
Yes, there is air conditioning, and it has always worked. The Y on the unit must have never been hooked up.
Should it be hooked up, what should I do
|
|
 |
New Member
|
|
Oct 8, 2009, 09:12 PM
|
|
If I go from G on the unit to G on the Thermostat, and W To W.
Does that mean I hook C to Rc/RH?
What do I do with the wire hooked to the R on the unit?
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 09:13 PM
|
|
The wire that is hooked to the C' terminal, is it from a separate cable at the furnace?
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 09:14 PM
|
|
R on the unit goes to Rh/RC on the stat with a jumper. W goes to W, G goes to G, regardless what color
|
|
 |
New Member
|
|
Oct 8, 2009, 09:16 PM
|
|
There's a labeled terminal board that has 5 connectors at the unit, those are labeled as W Y R G C and there are a couple of wired staked onto the back that lead into a box. I can only assume there are relays in there.
|
|
 |
New Member
|
|
Oct 8, 2009, 09:20 PM
|
|
The C is in the same bundle of wires that runs to the Thermostat. I traced it all out. It's just a little bigger that phone cable, but in a bundle the same way. I didn't see any splices on it. Just straight into the basement, across the floor joists, over to the hole where it terminates.
|
|
 |
New Member
|
|
Oct 8, 2009, 09:21 PM
|
|
Can I start crossing wires to see what comes on. Using the common? I would hate to have to do that, but if it won't damage my equipment, I would do it.
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 09:25 PM
|
|
If you short 24 volts to the common you will have problems, possibly short out the transformer
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 09:28 PM
|
|
It sounds like you have a wiring mess. Chances are they have a splice somewhere. Can you post a picture of the furnace circuit board and wiring connections? That may help me a little. If it's a straight shot from the furnace to the thermostat you can hook the thermostat as I posted earlier.
|
|
 |
New Member
|
|
Oct 8, 2009, 09:32 PM
|
|
I crossed wires, apparently the C was RC/RH. That was the green wire. Red was W, The one that was on R was apparently controlling the compressor somehow... It doesn't make any sense to me, and I KNOW it's not right, I'm just tired of messing with it.
|
|
 |
Ultra Member
|
|
Oct 8, 2009, 09:33 PM
|
|
How many wires are sticking out of the wall, and what color?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Control accounts questions
[ 7 Answers ]
Please help, I did not get the answer for this questions below !
The question is :
Opening balance for Trade payable is $142,600
Payment made during the year - $542,300
Discount received - $13,200
Goods return $27,500
And the closing balance for Trade Payable is $137,800
How much is the...
Trying to wire in fan and light control
[ 1 Answers ]
:confused: I purchased the hunter ceiling fan and light control for my hunter fan.I'm having problems installing the unit to the existing wires in the wall.There are 3 white wires that are togther,there are two black wire together , then there is a black wire by itself and of course the ground wire...
Looking for control wire on transformer
[ 5 Answers ]
I am installing a new HONEYWELL T8601D2019 - it won't power on.
I realize it needs a control wire connected to the C...
I can not figure out which wire off my transformer is the control.
I have three blue wires, a red, black, and white. Red, black and white are all connected to the unit in...
Birth control and Plan B Questions Please help!
[ 2 Answers ]
Hello, I just started to take Alesse-28, thirteen days ago, and I had unprotected sex on the 12 day, He did not ***** inside of me but I still took the extra precaution and called the clinic and I asked them if I was safe, they told me I wasn't. They advised me to take the Plan B pill to be extra...
View more questions
Search
|