    Boiler cycle time.
    My thermostat is set at 68. The boiler (Hot water) kicks on when needed. The problem is that it will turn off before it gets to the set degree, for a few minutes. Then it turns back on and continues to the set degree. Why is this and is it supposed to do this? Could it have anything to do with the High limit switch? If so, what can I do about it? I have the round thermostat, manual with Mercury in it.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Nov 1, 2006, 03:33 PM
    Sounds like the heat anticipator in the thermost is set wrong. Measure the amperage from W to R at the thermostat with the thermostat disconnected. Say it is .65 amps. Just under the cover is a small slider that says longer with an arrow and numbers, set the pointer to .65

    Good luck
    zoso43512's Avatar
    zoso43512 Posts: 40, Reputation: 2
    Junior Member
     
    #3

    Nov 4, 2006, 06:47 AM
    Ok sounds like a plan, but I am not too electrically inclined. SO a walk through would be appreciated. I have a DMT7 digital multimeter. It has a bunch of numbers, letters and symbols that it can be set to. And, yep you guessed it, I have no idea how to use it. Also, you say measure W to R. Is that the themostat wire or actually on the thermostat? I do know where the small slider and numbers are on the thermo like you said. Thanks again for any input.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 4, 2006, 07:33 AM
    Northern Heat gave you a good answer to a question I didn't even try to. In another thread, he said he would be gone, so I will try to help you use it. To measure amps, look for a position labeled A or mA. MA is milliamps, 0.65 amps would be 650 mA. Turn the pointer to it. If the meter has more than 2 places to plug in the leads, select Com and one labeled A.

    The next step will be easier if you have 4 hands or little alligator clips to snap on the leads. Remove the white or red wire from the thermostat. Connect one lead to the wire you removed, and the other to its terminal. Then turn the thermostat to heat and read the meter.

    If your meter doesn't match my directions, try to tell me what it does have.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #5

    Nov 4, 2006, 08:39 AM
    What number is the heat anticipator set at now? If this is a simple boiler without a control board, just find the amp rating on the gas valve, and add .05 amps for voltage drop in thermostat wire, (if over 30' long) set the anticipator to this number.
    zoso43512's Avatar
    zoso43512 Posts: 40, Reputation: 2
    Junior Member
     
    #6

    Nov 4, 2006, 12:59 PM
    Well I appreciate the help Heat and Lab. I tried to do what Lab told me, the only problem is I can't have a wire NOT hooked up to the thermostat and still attach the thermostat to the wall to do the test with the multimeter. I did however look at the gas valve stuff like Heat suggested. I "think" I have it right. It says Total Current .5 A. So I set the anticipator to the line between the numbers .5 and .6. So I will see what that does. Also, I have a hot water low pressure Boiler by Burnham-Model #P-205A-WNV. I read Heats post about giving the most info a person can to help with questions. The thermostat is a Honeywell (round) manual one. Thanks again for your time.
    zoso43512's Avatar
    zoso43512 Posts: 40, Reputation: 2
    Junior Member
     
    #7

    Nov 8, 2006, 02:37 PM
    Ok well I have done that and all is well. I still have the boiler shutting down though. Maybe I should clarify a little more to the problem. I set the thermostat to 66 while I am gone. I come home and turn it up to 68. The boiler will run for about 15 minutes and then shut down. The temperature will not be 68 yet. Then after about 4-5 minutes, the boiler turns back on for about 15 more minutes. Then shuts back off. It does this until the desired temperature is achieved. Once the temperature is hit, the boiler seems to run pretty normally. Is it the thermostat or is the boiler getting too hot and shuts itself off to cool down awhile or what? I have heard there is a high limit switch, could this have anything to do with this problem? Or is this how a boiler is supposed to operate? It is a Burnham 205A model. I just cycled it to see the numbers and I have 180 degree water temp. and 22PSI when it shuts down. The boiler ran for 17 minutes before it reached this.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #8

    Nov 8, 2006, 04:25 PM
    Quote Originally Posted by zoso43512
    Ok well I have done that and all is well. I still have the boiler shutting down though. Maybe I should clarify a little more to the problem. I set the thermostat to 66 while I am gone. I come home and turn it up to 68. The boiler will run for about 15 mins and then shut down. The temperature will not be 68 yet. Then after about 4-5 mins, the boiler turns back on for about 15 more mins. Then shuts back off. It does this until the desired temperature is achieved. Once the temperature is hit, the boiler seems to run pretty normally. Is it the thermostat or is the boiler getting too hot and shuts itself off to cool down awhile or what? I have heard there is a high limit switch, could this have anything to do with this problem? Or is this how a boiler is supposed to operate? It is a Burnham 205A model. I just cycled it to see the numbers and I have 180 degree water temp. and 22PSI when it shuts down. The boiler ran for 17 mins before it reached this.
    OK, now it sounds like the limit is shutting it down because the water reached temperature. It will take a while for the heat to radiate from the radiators to heat the room. The limits may be set to low. In the area I live you must have 2 limits, one comes with the furnace and one we install. I usually set the factory main limit at 190-200 degrees and the strap on limit at 180 degrees.
    zoso43512's Avatar
    zoso43512 Posts: 40, Reputation: 2
    Junior Member
     
    #9

    Nov 9, 2006, 03:58 AM
    Is this something I can check and change if necessary myself and how does it get done, or do I need to hire a qualified person? Thanks Heat!!
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #10

    Nov 9, 2006, 05:19 AM
    Quote Originally Posted by zoso43512
    Is this something I can check and change if necessary myself and how does it get done, or do I need to hire a qualified person? Thanks Heat!!!
    It may be nothing to worry about. Boilers always take a while to heat a house up. They just aren't as fast as forced air. As long as the pump stays running and the house gets up to the desired temperature, the gas valve cycling is no problem, all older boilers as they say, run on limit.
    zoso43512's Avatar
    zoso43512 Posts: 40, Reputation: 2
    Junior Member
     
    #11

    Nov 9, 2006, 02:02 PM
    Ok That sounds good to me. Thanks for all your help and hopefully I don't have any more Boiler questions for a while.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Boiler interlocks [ 2 Answers ]

Hi, I was wondering if anyone could tell me a little about boiler interlocks? I'm into my second year at college (level 2) and am interested in the heating side. At first I thought a boiler interlock was a wiring box but now I know it's a connection between the boiler controls. Trouble is I'm...

Boiler Pressure [ 5 Answers ]

I have just bled out the radiators to my hot water boiler. When I got to the last radiator upstairs, nothing came out. A lot of air, then nothing. I checked the pressure on the boiler and it read about zero. I turned on the system and the pressure went up to about 18 psi, that's about where it...

Computer won't start up first time, but will second time [ 8 Answers ]

So this is a completely different computer first off. When I press the power button, everything powers up, but the computer does not post, or beep. If you leave the computer on for like 10 seconds, turn it off, and then turn it immediately back on, it turns on, posts, beeps, boots into Windows...

Part time or full time resident? [ 3 Answers ]

Hi, I am a student in PA and spent about 3 months in New York during the summer for an internship. Since my primary domicile was still in PA (since I had to return for the next year of classes), am I a resident of PA for the full year or a part year resident? Likewise when I file state tax...


View more questions Search