    Boiler Cleaning-Hydronic
    I have a 125K BTU gas fired hydronic heating system in my house. My water is very hard. Over the past 15 years of opening the system to add zones, the boiler appears to have hard water issues. As it heats up, the boiler make loud kettling sounds. I have flushed the system, but that only has a minimal effect. I was told it needed to be flushed with muriatic acid. I procured a pump, fill tank and all of the needed hoses. I have plumbed over a drain and a fresh water supply line. My question is what % solution of acid should I use, how long should I recirculate and will the impurities pass through the boiler outlet spigot? Any info you can share I would appreciate. I also bought a supply of baking soda to neutralize the acid. I know this is a job for a professional , but in these troubled economic times sometime we have to do for ourselves.. Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 21, 2009, 07:22 AM
    First rule to follow

    Wear long rubber gloves and full goggles for your eyes. safety glasses will not protect your eyes. the acid can splash up under the safety glasses.

    ACID is dangerous to work with so have a fresh water supply available at all times and if you have a spill or get it on you flush with fresh water right away.

    Now on with the show.

    Safety data sheet READ

    http://www.boilercleaning.com/pdfs/HydrochloricAcid.pdf

    NEVER POUR WATER INTO ACID. While this acid could possible be poured eighter way I preferr not to take the chance.

    Are you using swimming pool grade acid?

    I need to know this or does the bottle have a % grade of acid label?

    Sorry about all the questions BUT acid can be a very dangerous to use.
    Dealmeinn's Avatar
    Dealmeinn Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 20, 2009, 01:07 PM

    I believe it is a 30% solution. I purchased it from Lowe's...
    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting a wood boiler to exsisting boiler [ 2 Answers ]

I need a plumbing diagram to connect a wood burning boiler to an exsisting primary boiler, exsisting boiler is apeerless 105/85 that is approx. 20 years old

Cleaning an Old Steam Boiler & Radiator Vent Valves [ 1 Answers ]

Hi, I have an old Utica Gas Steam Boiler. Do you recommend using Squick on old boilers as well? What do you know about Gorton venting steam radiator valves? Supposedly, they have a numbering system for each valve based on the location of each radiator in every room in your house. Thank...

Hydronic boiler controls [ 5 Answers ]

Hey my question is how do I test a transformer relay a limit switch Aquastat on a hydronic boiler using a multimeter. I need to know what I measure for what readings should I expect etc

Boiler Cleaning/ uneven room temperatures [ 3 Answers ]

Hello, I am new to this site. I have two questions, both pertaining to my gas boiler which was installed in October 2005. Last year we asked our plumber to come down and clean the boiler and he told us that it didn't have to be cleaned for five to seven years... is this true or should I have a...


View more questions Search