    Expantion tank filling with water
    I have a expantion tank on a forces hot water gas furnace that keeps filling with water. I replaced the last one with a new tank and it still fills with water. Does anyone know why and what can I do to prevent this. After it fills with water there is no expantion room and then the blowby valve gets intermittently released.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 21, 2009, 07:08 AM
    What type of tank do you have ? A standard type or a bladder tank?

    On a standard tank this is usually caused by to little or too much air in the tank. Usually draining the tank and then putting it back in service will fix the problem. Now if there is a air leak on any fitting above the hot water storage area of the expansion tank then it will loose its air charge.

    On a bladder tank (you can tell this style from the air charger scharader fitting on the bottom of the tank) the bladder goes bad and the tank fills up. Those you have to replace since draining them does no good.

    Your fill valve could be defective if it is allowing the pressure in the system to go above the 12 PSI or so level. This will cause the expansion tank to fill with too much water.

    This is what a bladder tank looks like.
    Attached Images
     
    Juliagrace1's Avatar
    Juliagrace1 Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 21, 2009, 07:22 AM

    Thanks HVAC1000. The picture you show is the same that I have. The new one filled with water. I did not check the pressure in it before I installed it. I thought they came charged. I will replace it again and check the pressure and if it fills again I will need to get someone more qualified that I.

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Sep 21, 2009, 07:34 AM
    Usually they are charged with 12 pounds from the factory but if you put a pressure gauge on it you will let out some of the charged air so be careful. My men carried a small manual air pump in the trucks for this purpose.

    Usually a bladder tank lasts for a good while but system design and tank placement on return or supply line can make a big difference in how long they actually last.

    Trick of the day

    Your diaphram tank should be charged to the same pressure as the boiler operating pressure. In most cases it is about 12 pounds BUT I have seen higher pressures on some systems.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Water tank not filling [ 11 Answers ]

I recently reinstalled a water tank and pressure switch and the tank doesn't seem to be filling and I have hardly any water pressure. I only get good pressure when the pump kicks in. I also installed a check valve to see if that would do anything.

New Hot Water Heater Wire Panel Filling With Water From Tank [ 2 Answers ]

I have recently installed a new electric hot water heater. I have connected all the wires properly, I have connected the piping in the correct manner, and filled the tank. I was about to flip my breaker to turn the water heater on, and noticed a little moister around the panel that the wires come...

Rainsoft Water Softener - Salt tank not filling with water? [ 1 Answers ]

Put a bag of salt in my softener today and it appeared to be way over the brine level. Checked on it a few hours later and still had dry pellets on top. Manually regenerated the system - no fill. Letting it go through its cycle now, but wondering if there's something I'm overlooking. There's...

Toilet tank not filling with water [ 5 Answers ]

Our toilet just decided to stop filling up with water. It eventually does fill up but the water is not "spurting" out of the tube, actually it's just dribbling... do I need to replace something or is this a job for a plumber... hopefully it's an easy fix and I'm hoping someone can help me... Thank...

Water tank not filling up [ 3 Answers ]

Today, we changed our kitchen sink. We drained the system, connected new taps,sink. Put water back on - first time ever no leaks. So off for a bath! We have no hot water.Having connected the cold valve on the washing machine to the valve on the hot water tap etc. we had a small amount of hot water...


View more questions Search