    Zone Valve Switch not Sending Signal to Boiler
    I have a 3-zone system. Two area heating and one hot water.
    The zone valves are honeywell V8043E1012.
    The area heating zones work fine.
    The hot water zone valve receives signal from thermostat OK and opens
    The water flow valve.
    However, the boiler and circulator do not receive the signal to fire up.
    When I touch the red lead wires from the valve switch, I hear a connection
    Being made and lost, as if there was a loose wire.
    Does that make sense? Is the Aux. switch accessible to check these connections?
    Or does this mean the entire valve needs to be replaced?
    Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 18, 2009, 09:14 AM
    Here is a link to your valve

    http://customer.honeywell.com/TechLi...0s/60-2133.pdf

    Yes there is an end switch in your valve.
    Yes it is replaceable BUT you will have to go hunting for a replacement switch since most supply houses only have the complete valve OR just the power head.

    You can test the end switch with a meter or as I sometimes do just jump the end switch wires. Now you have to make sure the valve is open before you jump the switch leads because you do not want your circulation pump to come on without a valve open to relieve the pump pressure. Sometimes I just flip the manual valve lever to the open position or activate the valve by the thermostat then jump the switch wires.

    I usually replace the valve since by the time the end switch goes bad the little shut off ball is bad but you do not have to as long as the valve was working OK before the switch went bad.

    I believe the switch is made by CHERRY Switch Company if my memory serves me correctly.

    If you replace the power head you will probably have to drain the system and that can be a pain to refill so if you buy the power head or the valve you could take the switch out of the new valve and put it in the old valve as long as Honeywell has not changed the switch style.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to replace boiler{ Honeywell} zone valve [ 6 Answers ]

Honeywell 40004850-001 isn't working. The lever to manually open valve freely moves back and forth. What do I need to do to replace this valve?

What kind of signal is this guy sending me? [ 2 Answers ]

There is this guy like . I think he likes me but I am not completely sure. He smiles at me every time I look at him. When we is talking to me his voice turns nervous, and when he is to close to me he never hold the eye contact for long, he only does this when I am a bit far from him. :rolleyes: He...

Are zone valves or zone thermostats possible with a steam boiler? [ 1 Answers ]

I have an old 4 story building with one thermostat controlling the steam heat to all floors. There is a commercial space on the ground floor and they are complaining that they don't get enough heat sometimes (and on occasion get too much!) They have suggested that there is some way to place a...

Changing Boiler from ONE zone into Two Zones [ 2 Answers ]

I'm considering buying a big renovated antique house in MA that has 14 rooms, 4,000 sq.ft Living area WITH ONE ZONE HEATING. All the windows have been upgraded and half of the rooms had insulation blown into the walls. The house has a burnham boiler, using natural gas with old fashioned steam...


View more questions Search