    Plug types
    I am replacing a wall unit AC for my parents that was running on a 220 line, 18,000 BTU standard three prong plug. I have purchased a new unit that is 25,200 BTU • 220 Volt 20 Amp Dedicated Circuit (Perpendicular Plug). I wasn ot aware of the plug diffrence. Do I need to return this or can I somehow alter their outlet receptical to accept this "Perpendicular Plug". I have been looking all over and there is no information anywhere! I was trying to do something nice and I am so confused and frustrated! Please help!!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 7, 2009, 12:40 PM
    You say the old unit had a "standard three prong plug". You don't mean a "standard" 120v plug do you??

    What did the prongs look like on the old plug/receptacle?
    ARWachtel's Avatar
    ARWachtel Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 7, 2009, 01:41 PM

    A tandem plug...
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 7, 2009, 02:07 PM
    Quote Originally Posted by ARWachtel View Post
    a tandem plug...
    I'm sorry but that tells me nothing.
    Describe the holes in the receptacle, or better yet post a pic.
    ARWachtel's Avatar
    ARWachtel Posts: 3, Reputation: 1
    New Member
     
    #5

    Sep 7, 2009, 02:15 PM

    I'm sorry... I'm really bad at this. I appreciate your help but I returned it for one that had a matching cord to receptacle. It was just easier!! Thank you anyway - you've been very kind.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Sep 7, 2009, 03:44 PM

    A plug chart is here. http://www.stayonline.com/reference-...ght-blade.aspx. What your probably looking at is a NENA 6-20 configuration.

    Note that one of the female sockets loots like a "T". This allows 15 A and 20 A 240 plugs to be inserted.

    12 AWG wire should have been run for 20 Amps.

    The blade configurations don't allow a 120 V stuff to be plugged into a 240 V outlet. The major difference between a 20 A 120 V and a 20 A 240 V is which side of the outlet the blade is horizontal.

    Usually 240 V receptacles have a single outlet. They are not usually duplex receptacle in the US.

    Now, does this help answer your question?

    Since, we are not exactly sure what it is.

    You also DO NOT want to use a Tandem breaker. i.e. Circuit Breakers - Tandem Breakers

    You want a 2-pole single handle or two interlocked handles.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Change 4 wire dryer plug to 3 wire plug [ 1 Answers ]

How to change a 4 wire dryer plug to a 3 wire plug

Can I plug my electric oven into a normal plug socket? [ 2 Answers ]

Can I plug my electric single oven into a normal plug socket?

12-3 wiring from gfi plug to outlet to plug in a 110v pool pump [ 5 Answers ]

Need to verify proper wiring for above 110v pool pump.

Black soot on the spark plug,is it the plug. [ 1 Answers ]

My lawn mower plug has black soot on it, what could be the cause of the plug fouling out? It is a 6.0 B&S motor, also is there a certain gap for the plug and if so what is it? This problem just recently came up after 3 years of use and I don't understand what happen.:confused:

Replace 2-plug GFGI with a 4-plug GFCI? [ 7 Answers ]

I am remodeling my bathroom and my wife wants a 4 plug outlet. She currently uses one for the hair dryer and one to charge her electric toothbrush. The intent is to add a lighted mirror or something else that uses little power. Would it be OK to replace the GFCI with a 4 plug GFCI? I suspect...


View more questions Search