    Alternative outlet grounding method.
    I know it might not be up to NEC code BUT as I see it: If your wiring does not have a separate bare ground wire (just hot, neutral) you should be able to change your 2 prong outlets to 3 pround polorized ones and ground it by taking a short piece of solid copper ground wire and jump from the green ground screw to the neutral screw (silver) or into the back of the neutral screw if available. After all a proper ground wire goes to the same grounding/neutral bar in the main box.

    As I said it would not be up to code but would this grounding serve the purpose. When you use a tester it shows the outlet properly grounded and not open ground.

    Advise
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 2, 2009, 06:41 PM
    You are 100% incorrect here. The fact that they terminate in the same place is completely irrelevant. Although is a common misconception, it can be a VERY dangerous one.

    A neutral carries current. A ground does not and should not.
    If you jump ground to neutral this brings the bare parts of the circuit to the same voltage potential as the neutral. Meaning, if you lose a neutral ahead of that receptacle the circuit will be looking for a way to find it's way back to the source. The source is the utility transformer. Since this and most other parts of the service are grounded to earth this is one path it will seek. Problem is the earth is a poor conductor, so you will get a shock, even a fatal one, but the earth, or other paths, will not be able to carry enough current to trip a breaker or blow a fuse.

    PLEASE, you or others reading this or thinking about this, DO NOT DO THIS!!
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Sep 2, 2009, 07:28 PM

    Your allowed to replace 2-prong outlets with a properly labeled GFCI (Labels come in the package).

    If you had a properly connected GFCI and you shorted neutral to ground UPSTREAM, it would trip.

    Ground is a reference and should not carry current unless it's a fault. It' the zero point for your CATV, your stereo, your plumbing fixtures etc. Under fault and normal conditions in YOUR PROPOSED SCENEREO, the grounds will be at different potentials.
    TGMcCallie's Avatar
    TGMcCallie Posts: 45, Reputation: 2
    Junior Member
     
    #4

    Sep 2, 2009, 08:16 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Your allowed to replace 2-prong outlets with a properly labeled GFCI (Labels come in the package).

    If you had a properly connected GFCI and you shorted neutral to ground UPSTREAM, it would trip.

    Ground is a reference and should not carry current unless it's a fault. It' the zero point for your CATV, your stereo, your plumbing fixtures etc. Under fault and normal conditions in YOUR PROPOSED SCENEREO, the grounds will be at different potentials.
    Why does the plug in GAF-500 show proper ground when you hook up as I suggested? Before I did it the tester showed OPEN GROUND.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Sep 3, 2009, 08:16 AM

    I'll urge you to read here: https://www.askmehelpdesk.com/electr...on-386501.html

    Just lost what I wrote.

    This tester: http://www.aemc.com/products/pdf/2117.60.pdf is used to probe ground currents. To be a ground, there must be little or no currents on the ground.

    If lightning struck your panel ground, all ground potentials in your house would go up. Lot's of devices would be destroyed.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Sep 3, 2009, 12:45 PM
    Quote Originally Posted by TGMcCallie View Post
    Why does the plug in GAF-500 show proper ground when you hook up as I suggested? Before I did it the tester showed OPEN GROUND.
    Because the tester is being FOOLED into thinking there is a valid ground.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Grounding outlet [ 6 Answers ]

Hey anyone How do I ground a 3 prong outlet and there are only 2 wires one black and one white. No green

Grounding an Outlet [ 22 Answers ]

I am moving into an older house that has only 2-prong outlets. Some are 3-prong, but they are not grounded (I have a power strip that tells you if it is gounded or not). I found this at Ace Hardware....

Outlet grounding [ 4 Answers ]

What problem would happen if the ground wire on an outlet was hooked to the netural white wire?

Adjusting entry alternative method [ 4 Answers ]

My net income is 1100 over what it should be and I can't figure it out. Help would be greatly appreciated. Here is the premise: Original Trial balance: Debits Cash 9500 Accounts Receivable 14000 Equipment 45000 Insurance Expense 1800 ...


View more questions Search