    Lennox G24M 3/4-100A-7 blower not start if in cool
    The gas furnace: Lennox G24M 3/4-100A-7
    SN:6398B17474

    In T-start, If heat and cool off, fan in on position, furnace indoor blower will run; Also try heat with fan on, blower also run;

    however switch T-start to cool, regardless fan in on or auto, when outside condenser is started, the furnace blower will be immediately stopped.

    ACBCool-NEUTRALS(any pin) = 0 VAC
    Y-C = 24 VAC
    R-C =24 VAC

    It looks K3 relay in circuit board is dead.

    From the diagram, K3 also controls ACBHeat; In my case, when fan is on, heat mode, the blower is started. I don't test fan in auto when heat mode case my house is hot.

    Is it possible that my heat is also broken in auto fan mode?

    Can I change the K3 relay only in circuit board?

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 22, 2009, 06:39 PM
    Usually the entire circuit board is replaced. I am not saying it cannot be done IF you can find a compatible relay but HVAC service persons just replace the board due to liability issues. I am sure there is a relay available that might work even if you have to use a remote add a relay type device and solder the wire extensions to the board. Been there done that but never on a customers equipment.
    zhuroy's Avatar
    zhuroy Posts: 6, Reputation: 1
    New Member
     
    #3

    Aug 23, 2009, 07:32 AM

    Thanks, sounds reasonable. I will see how I can proceed after my testing on heat/fan-auto is done.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox blower don't come on at all it clicks [ 1 Answers ]

2 green lights flash on the furnace, but the blower want come on. It clicks like its going to come on but don't

Lennox blower stopped working [ 4 Answers ]

Sorry for the double post but I couldn't find a way to edit the first one or delete it. Woke up nice and warm last night, upstairs ac had stopped working. Compressor outside is running, but no blower. Tried manually setting the fan from Auto to ON, nothing. Doesn't matter if I have it set to...

I need a 100A subpanel from parallel 100A main panels [ 3 Answers ]

I'm planning to install a low voltage driveway snow melt system that will require 70A (240V). I want to run this from a new 100A subpanel in my attached garage. My problem is that my 200A service is split into two 100A main panels. How would I accomplish this? My other option I suppose is to run a...

Lennox furnace no blower [ 1 Answers ]

Have lennox G20 Q4 furnace. Burners work when called for but no blower. Blower will not run when selected at thermostat. Had a new circuit board for the G20 Q3 furnace, installed it. Result was blower ran prior to burners igniting and blower would not go off after burner shut down. Changed...

Lennox furnace, blower not working [ 1 Answers ]

I have a 1000sqft town home with a Lennox furnace about 18 years old. My furnace blower is not working. I currently uneployed and job seeking and would like to avoid the cost of replacing the entire furnace. What sort of cost should I expect to replace the blower?


View more questions Search