    20 amp circuit connection
    I had an electrician install a 20 amp circuit to replace the 15 amp the microwave was connected to. He ran the 12 gauge wire to the junction box in the attic, but not all the way to the outlet. This does not make sense to me, since the wire from the junction to the receptacle is rated only for 15 amp. The breaker he installed is 20 amps, so I'm concerned the 15 amp portion of the wire may get too hot & not trip the breaker. Is this a safe configuration? Appreciate any help.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Aug 14, 2009, 04:01 PM

    You are correct in you concerns. All wiring on a 20 amp circuit must be 12 gauge. First check to insure that the cable from the junction box is 14 gauge. You want to make sure you are correct before faulting some one. Then call him back. This is a code violation and not a technical one. It poses real risk.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Aug 15, 2009, 04:41 AM
    This electrician should know better.

    I know what he will say, the amp load will never exceed the ampacity of the section of #14 wire, but still, it is just wrong.

    Tell the electrician to check with the local electrical inspector, with you as part of the discussion, and see what he has to say about this.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can circuit work well if we connect 12A load to 20A circuit? [ 5 Answers ]

Hello: I have several equipment which are around 12A. I just can connect them to 20A circuit. But I am not sure if circuit will trip well under overload and short circuit. I know 15A is perfect.But,I don't have 15A circuit Thanks for everybody.

Connection of fan to 3-way electrical circuit [ 2 Answers ]

I am connecting a new Hampton Bay ceiling fan to a 3-way electrical circuit (2 black and 2 white service leads to the fan). Instructions say to connect both the blue and black leads from the fan to the black power source. Since I have two black power leads, I tried putting the blue on one and the...

Converting 240v circuit to a 110v circuit [ 6 Answers ]

I have a 240 circuit, to make it a 110 circuit. I need to remove one of the hot wires?

Connection of tub to main 3" circuit pipe in bathroom [ 1 Answers ]

I have two questions for reconnecting a 1.5" line from a tub to a 3" line that is part of a circuit wet vent in bathroom (tub, shower, lav and toilet all connected to 1 horizontal 3" line vented at the begining and end by two individual vent lines). 1. what angle should the tub combo/Y fitting...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search