    Wiring to GenSet
    Hello,

    I'm starting a project to hook-up a optional stand-by generator. I have all the wiring for the transfer switch, service panel & essential sub. I need to run about 25 feet of 6/3 from the transfer switch to an outside wall along with a 14/2 (A/C power to the battery charger) and two 18 wires for the start control circuit. I can run standard romex for the 6/3 and 14/2 and appropriate cable for the two-wire start (most likely a 6/8 conductor 18 cable).

    I obviously need to bring this outside to the gen-set. My plan is to use a LB to 1 1/4 or 1/12 liquid-tight(LT) (max 6 feet). Straight LT connection from the PVC LB to the LT and then a 90 deg LT fitting to the generator.

    How do I make the transition from inside to outside wiring? I'll be connecting the LB to PVC conduit to penetrate the wall and then go into a large junction box. Can I then splice the romex to the THWN I plan to run in the Liquid Tight in that junction box? I've seen some "pre-wire" kits that run the romex right out to the gen-set, I suppose this is allowed because the whole assembly is listed.

    I'd like to hear some feedback about the right/safe way to do this.

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 20, 2006, 12:31 PM
    Your plan is fine, exactly the method most installations would be done.

    I just did a 12KW genset, the interior line was about 20 feet, then about 5-6 foot on the exterior to the gen. I used flexible conduit inside and LT outside, simply coupled together using an LB, used no junction box and no splices, by pulling through the 3-#6, 1-#10 ground, and 2-#14 starting circuit THHN straight through 1" flex.
    joemoor's Avatar
    joemoor Posts: 5, Reputation: 1
    New Member
     
    #3

    Oct 20, 2006, 05:14 PM
    tkrussell thanks for the reply.

    I'm seeing the straight pull of THHN as the better and possibly cheaper way to get this done. One question the inside conduit, you used ENT? (Smurf tube?) did you go that route because it's easier than Sch 40? I've never used ENT and it's not required in my area (Northern NJ). I've read through Carlon's site and the snap connectors are an easier alterenative to glue. I'd be pulling the 2 #14's as the AC supply to the battery charger & carb heater, I'd pull two more #18 for the start circuit (30VDC ~ 2AMP). 1 Inch should have the proper fill capacity, now I just need to find it.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 20, 2006, 05:18 PM
    I used metal flexible conduit and metal liquidtite, and connectors for each. This material is not available at home centers, only at electrical supply houses.

    I used a rigid coupling and a 6" steel GRC nipple into the LB ,transitioning at the point leaving the basement.

    ENT and nonmetallic LT is fine also, just be sure to include a #10 green for the ground.
    joemoor's Avatar
    joemoor Posts: 5, Reputation: 1
    New Member
     
    #5

    Oct 21, 2006, 01:43 PM
    Ok,

    Can I ask you to double-check me again?

    I went to the electric supply to purchase some flexible metal conduit. Price and ease of install along with the guy working the counter drove me to LFNC-B, the functional equivalent for flexible PVC?

    So it's cheaper, easier to install (for me) etc..

    So the new plan LFNC-B about 27' from ATS to inside LB, standard PVC fittings no LT fittings inside.

    LB inside to outside LB via PVC conduit. LB outside to LFNC-B again this time with LT fittings.

    The LFNC-B is 1 1/4 so my fills are OK based on what I'm pulling 3-#6(H,H,N from gen), 2-#10(G for gen and new outlet in gen housing),2-#12(H,N for new outlet) & 2-#14(start control).

    My #3 & #12 are de-rated to 80% because of > 3 cc counductors.

    So would any sparky or AHJ get a chuckle from the LFNC-B inside instead of Sch 40? the are I needed to run through would have made Sch 40 prohibative (existing runs, plumbing, etc... It's bought, installed (not glued yet) and ready to pull wire...
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 21, 2006, 03:39 PM
    Only problem is with the inside connectors, you probably have Sch40PVC fittings, and these are not rated for LNMC. They will probably work OK, but an inspector may fail the installation. Any electrical part is listed for their specific use, a good inspector will catch this.

    Support the flex every 36" with straps for that size raceway.Any conduit support clip sized for 1-1/4' rigid or heavywall will work.

    The conduit fill is fine, and when derating #12 THHN, start with 30 amps as the full ampacity and derate from there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring [ 1 Answers ]

I am connecting my wiring to a new motherboard, I have a wire running from the front of the case it says S/B SW, but the manual for the mobo has nothing to connect to that, does anyone know what connections to go to or what that means. Thanks :)

AC Wiring [ 1 Answers ]

I have an eletrical AC unit with a 28.2 amp compressor and 3.1 amp fan. The nameplate on the unit specifies minimum circuit breaker size of 39 amps and maximum time-delay fuse of 60 amps. Two questions: 1) what size breaker do I need for this unit in breaker box? And 2) what gauge wire do I run...

Wiring Help [ 4 Answers ]

I'm wanting to run electric from garage to shed. Want to have an outlet always hot and a light controlled by a switch. How do I do this? Any help and diagram appreciated. :confused:

Help with wiring [ 6 Answers ]

Hi Folks, I am building a vivarium and need some help re wiring plan. I am going to have a piece of board with 8 standard single wall plug sockets and switchs on it which will be attcahed to the back of the vivarium. Now I want to wire them so they can be used as normal but the only source of...

Wiring [ 1 Answers ]

Sorry, I was tired when I posted the last thread. I meant to say a light was being feed by a 12 gauge wire from a 14 gauge line with a 15 amp breaker. Is this OK?


View more questions Search