    Arc Fault Troubleshooting
    New Arc Fault Circuit breakers installed. On 1 circuit all wiring & circuitry checks out good. Circuit stays alive when nothing plugged in. Circuit stays alive when all devices plugged in so long as they are not on. However, whenever a device is plugged in & it is switched to on, the arc fault breaker trips. It does not matter which device it is as every device has the same impact, one at a time. Breaker changed out with known to be good breaker, same results. Once a lamp, fan, electronic device, surge protector alone, you name it is plugged in & turned on, the breaker trips instantly. Common part of circuit is not shared with another circuit & returns to the common bus bar by itself.
    Any detailed thoughts & solutions?
    Thank you
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 17, 2009, 11:09 AM

    Can we please have some pics of the breaker's installation. Also, what is the static load of the circuit (15 or 20 amp)? What is the AWG of the cable being used in the circuit?

    You say the entire circuit look good, how did you ascertain that? Did you pull all of the outlets along the circuit and verify the condition of the cable and connections?
    docarch1's Avatar
    docarch1 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 17, 2009, 11:42 AM
    Static Rating is 20 Amps.
    Voltage is 120 VAC
    AWG is 12 ga.
    Circuit holds with all loads connected but not on (individual)
    Circuit holds with complete load side disconnected.
    Curcuits tests appropriately.
    Visiual inspection of wiring, connections, & other devices is good.
    Circuit holds with all loads disconnected (individual)
    Circuits trips immediately when load devices turned on.
    Examples of devices are older model (85 possibly) non tube type TV, floor lamp, fan/airpurifier type device, SATV receiver, isolated surge protector, stereo receiver, dual cassette deck.
    Other known to be good AFCI breaker tested on circuit.
    No phot available, but photo would should proper Square D QO AFCI breaker installation installed above two other AFCI breakers on bus with breaker nuetral connected to independent nuetral bus & incoming nuetral & hot from circuit homerun connected to AFCI breaker accordingly.
    No apparent shared nuetral load.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jul 17, 2009, 02:12 PM

    They will trip like a GFI as well, If the circuit sees an unbalanced load like 2 circuits sharing a neutral, it will trip.
    Hot and Neutral MUST draw same amount of current.
    Neutral may be touching ground somewhere.
    If hot was touching ground, the breaker should trip.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Troubleshooting. [ 2 Answers ]

I'm trying to trouble shoot an older computer I inherited. I am completely new to PCs. At any rate it has two problems that are possibly relateed. 1. The image the monitor (I have tried 2 different working monitors) has a bunch of red (sometimes grey) vertical lines across the screen which...

Arc Fault troubleshooting [ 4 Answers ]

I've got a new arc fault circuit that trips immediately. I've switched out the breaker with the same results. How does one locate the problem in the circuit?

Second HD troubleshooting [ 1 Answers ]

Ok, here's the skinny... Intstalled my girlfriend's HD (Maxtor DiamondMax Plus 9 80GB ATA/133 HDD) onto my computer as a 2nd HD(slave). All jumpers are set correctly, all cables are correct (not the 1st time I've done this). Everything works fine, it's detected and I do have access to it. ...


View more questions Search