    Adding a 220volt outlet to existing 220v 4 wire for Hot tub
    Previous owner installed a 220v wire box outside of Garage for Hot tub. It is run through the Garage panel inside to out. Just the wires not outlet.

    I want to install a 3 wire outlet so I can plug in my 220v welder. Why to I have an extra wire.. One red I assume is hot, one white I assume is neutral, One black > hot.. and finally a bare unshielded wire I assume must be ground.. I really haate to assume when it comes to 220v 50 amp.:confused:

    Hello,

    I am attempting to install a 3 wire 220v Outlet for my Welder to an existing 220v electrical box on my Garage that was apparently used for a Hot Tub at one time. The box is outside of Garage. What is confusing to me is there are wires going to the box from the inside breaker panel, and wires coming from the ground going to the outside electrical box also.. Why 2 sets of wires..

    I believe I should use the Red & black as hot, and the bare as a ground. What should I do with the white wire..

    Thanks in advance... Joe:confused:
    Attached Images
     
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Jul 5, 2009, 07:45 PM

    You are right in thinking that the RED and the BLACK are the two hot lines and the WHITE is neutral and the bare copper wire is the ground. Make sure you take this ground all the way to the metal on the pump housing.

    If you have a volt meter you can go out to the breaker box and double check the wires at the breaker.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Jul 5, 2009, 08:09 PM

    The lower wires probably went to the hot tub a few feet away by way of an underground conduit.

    Other issues:

    The panel may not be made for outside use.
    Since this is a 3 wire fed sub-panel, ground and neutral should remain separate. They don't appear to be. Usually you need a ground lug kit to make that happen and a green ground bond screw should be removed.

    Your welder doesn't need the white wire. If those wires at the bottom were running to "the welder", then the white could be capped.

    There was proobably a two pole GFCI breaker there which requires a neutral connection, so all the wires at the bottom went to the spa breaker.

    The issue I see, although wires are obscuring the lower section is that the neutral (white) from the top/feed is not isolated.
    keesanka's Avatar
    keesanka Posts: 3, Reputation: 1
    New Member
     
    #4

    Jul 5, 2009, 08:19 PM

    OK, I feel really dumb now.. Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Jul 5, 2009, 08:19 PM

    <threads merged>

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Converting 220v 4-wire outlet to 3-wire [ 2 Answers ]

I bought a new drier with the "inverted V" 3-wire power plug. The drier outlet I have is like an overgrown version of a 110 grounded outlet, with 2 vertical 110 prongs and a ground socket. I bought a V-socket to accommodate the new drier plug, but when I shut off the breaker and opened up the old...

Adding outlet to 220v circuit [ 2 Answers ]

Learning as I go, so please forgive me if this is rudementary. I will explain what I need as best I can. I need to add two new outlets to an existing 10-3 wire 30 amp 220v circuit in my shop. Currently, the circuit only has one outlet on it that is in the wrong area of the shop for my needs. ...

Adding new switched outlet to existing circuit [ 4 Answers ]

I am completing a basement remodeling and am reaching the point where I'm about to install drywall. At the last minute, I realized I should add a switched outlet (both receptacles will be controlled by a single switch) at a location in my rec room. I installed the two gang boxes and ran cable...

Adding 4 wire service to an existing 3 wire config [ 4 Answers ]

I'm currently researching wiring a hot tub 240v 4 wire 50amp, but have an older Federal Pacific box as the main. Is there a relatively simple way to change a 3 wire system to a 4 wire where the hot tub connects. Eventually I will dump the FP box and rewire, but now is the time for tubbing :) ...

Connecting ground to 220v 3-wire outlet [ 8 Answers ]

I am trying to connect my bandsaw to an old-style 3-wire 220v dryer outlet (2 hot wires, 1 neutral). My bandsaw has no neutral wire. Do I connect the ground from the machine to the neutral socket?


View more questions Search