Jun 29, 2009, 08:05 PM
|
|
White-Rodgers 1E56W-309 thermostat to Honeywell VisionPRO 8000 programmable thermosta
I am replacing white-rodgers 1E56W-309 thermostat to Honeywell VisionPRO 8000 programmable thermostat. I have 1H/1C system in my house. However, my furnace is used both for heating and cooling. I have read the installation manual for the white-rodgers thermostat and looked at the current thermostat installation. It is a 5-wire 1H/1C heating/cooling system. Now, a 5-wire heating/cooling system for a White-Rodgers 1E56W-309 means there is a transformer for heating and a transformer for cooling. However, because of the single furnace, I am afraid the system could be a single transformer system. Folks, it is possible to have a 2-transformer system with a single furnace?
Thanks in advance,
Eric.
|
|
 |
New Member
|
|
Jun 29, 2009, 08:19 PM
|
|
Additional information.
The five independent wires connected to the White-Rodgers 1E56W-309 are: RC, RH, W, G and Y.
Thanks,
Eric.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 30, 2009, 12:03 AM
|
|
And what is your question?
No model number with the ending of 309 listed on the WR site
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 30, 2009, 12:06 AM
|
|
Yes it is possible to have a two transformer system with a single furnace because in some cases the A/C unit has its own transformer making it a two transformer system. They are a bit rare but my system for the main house section does have two transformers.
If you only have one transformer you usually jumper RH-to-RC
|
|
 |
New Member
|
|
Jun 30, 2009, 05:07 AM
|
|
Thanks hvac1000. You are really a Pro. The RC and RH terminals are not jumpered, so it is a 2-transformer system. Thanks a million and I shall replace the thermostat this evening and send you an update. Again, thanks.
Eric.
|
|
 |
New Member
|
|
Jun 30, 2009, 07:53 AM
|
|
Make sure you turn off the power to the systems before rewiring. It is easy to short the system out when replacing the thermostat. Good luck!
Tim Burke, White-Rodgers.
[email protected]
|
|
 |
New Member
|
|
Jun 30, 2009, 08:44 AM
|
|
Thanks for your advice.
Cheers,
Eric.
|
|
 |
New Member
|
|
Jun 30, 2009, 10:20 AM
|
|
Folks, I need a little help. On mu current White-Rodgers 1E56W-309 (Obtained from the inside cover of thermostat), the RED wire is attached to RH, black wire to RC, then white wire to W, green wire to G and yellow wire to Y. According to the installation instructions for the Honeywell VisionPRO 8000, the RED wire from the current thermostat, should be connected to C on the Honeywell VisionPRO 8000. Since I have RC and R terminals on the Honeywell VisionPRO 8000, I think it is logical to say that the RED wire should go R in the absence of RH on the Honeywell VisionPRO 8000, since the old thermostat had no C terminal. Please advise. I need to get this off the way before I install Honeywell VisionPRO 8000. Anyway, the terminals on the Honeywell thermostat are: RC, R, W, G, Y and C. The terminals on the White Rodgers 1E56W-309 thermostat are: RC, RH, W, G and Y. There is no jumper between RC and RH. Therefore it is a 5-wire heating/cooling system.
Thanks,
Eric.
|
|
 |
New Member
|
|
Jun 30, 2009, 02:14 PM
|
|
hvac1000,
You are a genius. I came back and read one of your posts that said that keep it simple and match the existing wiring to your current one. I followed this simple advice and installed the Honeywell VisionPRO 8000 and it is working as I am writing to you.
Both furnace and air conditioner are working and I cannot thank you enough. Wherever you may be, may God bless you immensely. I already had the pdf installation manual for the White-Rodgers 1E56W-309. I needed somebody to confirm the two transformer system with a single furnace, you were the one that was able to explain stuff black and white for me. Again, thanks a million for your good work.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jun 30, 2009, 04:20 PM
|
|
Glad you got it working.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Changed over from White Rodgers Thermostat to Honeywell thermostat
[ 3 Answers ]
I have a White Rodgers 2 stage heat/1 cool model 1F58-58 heat pump thermostat that I have changed over to a Honeywell programmable thermostat model RTH7400. Did all the correct wiring as stated in the books but when set to cool, the heater kicks on instead of the central air conditioning. What...
Changing over from White Rodgers Thermostat to Honeywell thermostat
[ 3 Answers ]
I have a White Rodgers 2 stage heat/1 cool model 1F58-58 heat pump thermostat that I want to change over to a Honeywell programmable thermostat model RTH7400. I need help in trying to figure out the wiring part of this whole thing. Can someone out there please help. I would certainly appreciate...
Replacing White-Rodgers Thermostat with Honeywell Digital
[ 7 Answers ]
I am replacing a 13 yr. old White-Rodgers Mechanical thermostat (couldn't find model # on website) with a Honeywell 5-1-1 Digital thermostat.
The wiring was as follows for White-Rodgers:
Green = G
Yellow = Y
White = W
Red = RH jumpered to RC
The Honeywell has terminals for
White Rodgers 1F76W357 to Honeywell RTH3100C Thermostat
[ 1 Answers ]
I have on old White-Rodgers 4 wire single transformer system I believe. Model 1F76W357.
I am installing a Honeywell RTH3100C non programmable thermostat.
Wires on the White-Rodgers are:
RC RH (Jumpered inside the thermostat)
W
Y
G
Which Thermostat? - White-Rodgers or Honeywell
[ 5 Answers ]
I am looking at buying a new thermostat and I am trying to decide which to buy the Honeywell 8000 or the White-Rodgers 90 series (1F95-1277).
I am also trying to determine what the difference is between the two White-Rodger 90 series models (1F95-1277 and the 1F97-1277). I know what the...