:(:(I have an old gas furnace (air ease) the blower motor won't turn on for the heat or the a/c. I hear it click when I switch from the two and the a/c and the heat are working but the blower is not, I'm currently laid off so I need cheap fix it answers thanks,JOE,P.S. my dogs chewed up the wire (Low voltage) outside to the a/c but I fixed it,(Rather simple) it worked for a short while then the blower stopped working ,maybe coincidence... the blower is not seased I can turn it by hand it moves nice and smooth...
|
|
 |
Ultra Member
|
|
Jun 25, 2009, 06:57 AM
|
|
Does the motor hum and/or get hot? If so, you might try replacing the capacitor. It should be around $20 or so.
You might also refer to this post, this post, and this post.
Best of luck,
WallyH
|
|
 |
New Member
|
|
Jun 25, 2009, 10:07 AM
|
|
The blower motor is not hot moves freely, I cannot see anything resemling a capacitor by the blower but I took a cover off on the outside of the furnace and this looks like a capacitor inside it unplugs and has 5 pronges that plug in it is a honeywell has 24v 59/60hz on the sidecontact ratings 12afl 60 alr 120vac
6afl 35 alr 240vac
And a few more like this is this what I should replace Joe
|
|
 |
New Member
|
|
Jun 25, 2009, 11:01 AM
|
|
I removed the motor also do not see a capacitor attatched on or near the blower there is only two wire going to the blower and that's the power, those wires go back to a junction box with a transformer on it...
|
|
 |
New Member
|
|
Jun 25, 2009, 11:09 AM
|
|
I checked the voltage going to the motor and its 116 apr is the motor bad?
|
|
 |
New Member
|
|
Jun 25, 2009, 11:10 AM
|
|
My fan on my centeral air unit won't spin but still makes a noise like it wants to come on what could be wrong with it?
|
|
 |
Ultra Member
|
|
Jun 25, 2009, 02:03 PM
|
|
 Originally Posted by jdubya5
the blower motor is not hot moves freely, i cannot see anything resemling a capacitor by the blower but i took a cover off on the outside of the furnace and this looks like a capacitor inside it unplugs and has 5 pronges that plug in it is a honeywell has 24v 59/60hz on the sidecontact ratings 12afl 60 alr 120vac
6afl 35 alr 240vac
and a few more like this is this what i should replace Joe
This sounds like a relay. When the thermostat is calling for air, do you hear the relay click? Can you safely close the contacts (with an wooden stick or something non-conductive)?
WallyH
|
|
 |
Ultra Member
|
|
Jun 25, 2009, 02:04 PM
|
|
 Originally Posted by jdubya5
i checked the voltage going to the motor and its 116 apr is the motor bad?
It might be. We want to be sure before declaring it dead, though.
WallyH
|
|
 |
Ultra Member
|
|
Jun 25, 2009, 02:06 PM
|
|
 Originally Posted by jdubya5
i removed the motor also do not see a capacitor attatched on or near the blower there is only two wire going to the blower and thats the power, those wires go back to a junction box with a transformer on it ...
Is there a "hump" on the side of the motor? Sometimes, the cap is on the motor itself.
WallyH
|
|
 |
Ultra Member
|
|
Jun 25, 2009, 02:06 PM
|
|
 Originally Posted by laurie772006
my fan on my centeral air unit wont spin but still makes a noise like it wants to come on what could be wrong with it?
Please refer to the links in my original answer.
WallyH
|
|
 |
New Member
|
|
Jun 25, 2009, 03:34 PM
|
|
There is no hump on the motor I took the motor off wired it directly to a plug and it did not work, unless there is a capacitor inside the motor I don't think it has one...
|
|
 |
Ultra Member
|
|
Jun 26, 2009, 01:44 AM
|
|
 Originally Posted by jdubya5
there is no hump on the motor i took the motor off wired it directly to a plug and it did not work, unless there is a capacitor inside the motor i dont think it has one...
That was a good test. Based on that, I would tend to believe that your motor is bad. If you're getting 116 volts to the motor in the furnace, and plugging the motor into the AC directly doesn't make it run, the motor is suspect. Take it with you to an industrial supply house to get a replacement. At least you'll save a hefty labor charge.
Best of luck.
WallyH
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Blower motor won't turn on
[ 4 Answers ]
:(:(I have an old gas furnace (air ease) the blower motor won't turn on for the heat or the a/c. I hear it click when I switch from the two and the a/c and the heat are working but the blower is not, I'm currently laid off so I need cheap fix it answers thanks,JOE,P.S. my dogs chewed up the wire...
Rheem furnace blower motor won't turn on
[ 2 Answers ]
My furnace blower motor will not turn on. The troubleshooting guide says to replace blower motor but the diagnostics says the Limit Switch is Open any ideas
Furnace Blower Motor will not turn on.
[ 2 Answers ]
After a week away from home to deal with a funeral I come home only to discover the blower motor in the furnace will not turn on either by auto or manual on the thermostat. I go into the attic and pretend to know what I'm looking for but do not. The circuit diagram is not very ledgable on the...
Oil furnace blower motor does not turn on
[ 1 Answers ]
Oil furnace blower motor does not turn on, in the "auto" setting, but will turn on in the "on" setting. Replaced thermostat, but still the same problem.
Blower motor won't turn off
[ 3 Answers ]
I have a Carrier central air and furnace model 28GS 036 000. This problem began with turning the furnace on for the first time this season.
With the thermostat off and the fan set to auto. The blower motor keeps running. Adjusting the temperature on the thermostat and selecting cool or heat does...
View more questions
Search
|