    Main breaker in sub panel?
    I am wiring a sub panel in a pole barn that is 30 feet from the house, my questions, is I purchased a 100 amp main lug panel with 6 spaces for breakers, can I run 6-3 with ground from main panel box in house and put a 60 amp breaker in main panel box in house and use the sub panel box in barn with only 2- 20 amp beakers to run lights and receptacles , do I need a main breaker in sub panel to disconnect the power in pole barn? Also do I wire a ground rod at the sub panel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 21, 2009, 10:14 AM
    You can use up to and no more than six circuit breakers as the REQUIRED means of disconnect for this building. Once 7 circuit breakers are needed, then one main will be required.

    Yes at least one ground rod is needed. Check local codes, some states require at least two.

    Otherwise your plan is fine.

    Just in case, do not use NM-B cable outdoors, not allowed in wet or even damp locations.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 21, 2009, 10:18 AM
    Also, keep in mind that #6 NM cable is only good for 50A, NOT 60.
    skinned knuckle's Avatar
    skinned knuckle Posts: 2, Reputation: 1
    New Member
     
    #4

    Jun 21, 2009, 03:09 PM

    Thanks Guys, I appreciate your help I am going to work on this tomorrow.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Difference between Main Lug and Main Breaker Panel [ 8 Answers ]

What is the difference between a Main Breaker Panel and a Main Lug Panel and can either be used in new residential construction.

Replace a two pole breaker in main panel box [ 1 Answers ]

I need two replace a bad two pole breaker in main panel boxwhat tools do I need

Main Breaker at bottom of Panel? [ 5 Answers ]

On a 200 Amp, Main Breaker Panel, If you are changing panel out, and wires are short, and instead of bugging on more, can Main Breaker be at bottom of Panel to eleminate Splicing, Providing switching is side to side. Verticle breaker, down would be on and not code?

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Main breaker panel [ 1 Answers ]

Hi, I'm looking for a 100 or 125 amp 30 or 32 space main breaker panel(not a mlo) and have been unable to find one. Can some one tell me where I can get one with the main installed? Thanks Jim


View more questions Search