Unless your friend is a licensed qualified electrician, do not take any advice from him/her.

Originally Posted by
brian9393
some one that is a friend was looking at how many 20 amp were in the box and said to me that my pannel box would not pass code because it has 750 amps in breakers
Adding up the amp ratings of all the circuit breakers in any panel means absolutely nothing.
Can you explain what your trying to do?
The 200 amp rating of the system you have was determined, or should have been,by performing load calculations, and should have some reserve ampacity for future load.
Any idea of the new load? Has anyone done the calcs to see if your panel or service has the capacity to add load?