New Member
|
|
Oct 7, 2006, 06:24 PM
|
|
AC compressor not running
My AC froze up and stopped cooling.
I turned the ac off, and put the fan in run mode until the ice melted.
When I turned the unit back on, the compressor did not come on.
It is an Amana, just over 3 yrs old.
Bruce
|
|
|
Ultra Member
|
|
Oct 7, 2006, 06:31 PM
|
|
Is anything on the outside running.
|
|
|
New Member
|
|
Oct 7, 2006, 08:08 PM
|
|
The outside unit is not running.
The fan unit inside the house turns on when the Auto mode kicks on.
|
|
|
New Member
|
|
Oct 7, 2006, 08:23 PM
|
|
I went to the Amana web site to review their warranty, but
Could not find my model listed, a BMA42F00A.
Any idea how well they take care of problems like this?
|
|
|
Ultra Member
|
|
Oct 7, 2006, 08:31 PM
|
|
Your serial number would give a hint to what the age of your unit is but this does not sound like it will be that serious of a problem. Have you checked your fuses or your breakers which ever you have for the outdoor unit. Check those and you need to check with a meter that will show you how much voltage there is instead of a light that will light if there is voltage. With the current off stick a stick or something in the unit to the fan blade and see if it will turn easily.
|
|
|
Full Member
|
|
Oct 7, 2006, 08:36 PM
|
|
If,. It is still under warranty... do nothing and call the person who installed it... any work on AC by you will kill the warranty
|
|
|
New Member
|
|
Oct 7, 2006, 08:51 PM
|
|
I have done nothing but shut it down and let it defrost.
The serial number is 02101 22104.
All the Circuit breakers on the hous panel are set.
I did not see an CBs on either the compressor or the inside unit.
Where would I check the voltage for the compressor?
|
|
|
New Member
|
|
Oct 7, 2006, 08:55 PM
|
|
Also, the compressor blades turn freely.
|
|
|
Ultra Member
|
|
Oct 8, 2006, 05:52 AM
|
|
Have you look at or tested the contactor in the outside unit? Could be the coil in it is bad and not pulling in the contacts
|
|
|
New Member
|
|
Oct 8, 2006, 07:11 AM
|
|
I have not checked anything on either unit of the ac.
No schematic to follow or voltage chart.
|
|
|
Ultra Member
|
|
Oct 8, 2006, 07:20 AM
|
|
The contactor is in the condensing (outside) unit It is a rectangler Box with the incoming 240V and when a call for cool from thermostat the coil will energize and the contacts will close passing current to other componets. Be very careful as you are dealing with high voltage. If not comfortable or experienced call a tech. Safety is most important
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Compressor Map
[ 2 Answers ]
I am working with refrigeration systems for some research. I am looking at the compressor map and have been told that a correction factor of .75 is fair to assume for conditions outside of the map's designated superheat and intake temp. Does anyone know where I can obtain any articles to support...
Compressor
[ 2 Answers ]
Hey we were out of town then came back and the ac breaker was tripped after turning on the fans run but the compressoe never kicks in we never had any problems with this unit before can some one give us some ideas were to start thanks:D
Air Compressor
[ 3 Answers ]
I have a new air compressor for my hot rod fabrication. The specifications are as follows,
5.5hp 80gal 24amp 240v. My question is, it calls for a 30 amp breaker and time delay fuse, Type "T". I am running 6/2 wire to supply the unit, it is about 90 ft from the main panel so we ran 6/2 for minimal...
AC Compressor stopped
[ 2 Answers ]
My compressor has completely stopped. I can here it surge like it wants to, but nothing happens. I am inside the house when I here this. The unit in the house works, just not the compressor outside. It is new, as this is a new residence, not even a year old. It is 100 degrees here today in...
AC Compressor Vibration
[ 3 Answers ]
Our new Ashwood Builders home has 2 AC compressors mounted outside on a small concrete slab that is connected to the main foundation. All the other homes in this new neighborhood that I've checked have a small gap between the compressor slab and the foundation. Even though the new compressors are...
View more questions