    I want to put up a sub panel in a work shop.
    I would like to know what size feeder wire do I need to run to a new CH 125 amp sub panel located 165' max a way from the main panel. I will have a small 110 welder and some day a 220 welder, running small tools, air comp. lights in the shop and a stove for an out side kitchen.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    May 23, 2009, 07:57 PM
    It depends on what breaker you intend to use to supply the sub panel. For what you plan on using, a 100 amp breaker in the main with #0 would suffice.
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #3

    May 23, 2009, 08:28 PM

    Sorry to say they do not make a #0 wire size. If you are burying the wire directly in the ground to your sub panel then you can use #2 Quadplex
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #4

    May 23, 2009, 09:37 PM
    Quote Originally Posted by jerro View Post
    Sorry to say they do not make a #0 wire size. If you are burying the wire directly in the ground to your sub panel then you can use #2 Quadplex
    No. 0 wire is commonly called 1/0, or "one ought."

    No. 00 wire is 2/0, 000 is 3/0 and 0000 is 4/0 respectively (spoken "two ought," three ought," and "four ought.")
    marshlandwaters's Avatar
    marshlandwaters Posts: 2, Reputation: 1
    New Member
     
    #5

    May 24, 2009, 10:13 AM
    Quote Originally Posted by ohb0b View Post
    No. 0 wire is commonly called 1/0, or "one ought."

    No. 00 wire is 2/0, 000 is 3/0 and 0000 is 4/0 respectively (spoken "two ought," three ought," and "four ought.")
    Thanks to all for the HELP!! :

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need to run a sub panel to my attached garage for woodworking shop. [ 5 Answers ]

Hi all! I am a woodworker and need to install a sub panel in my attached garage. The main is a 200 amp panel and my home was built in 2001. I live in AZ and spoke with the city who said they go by the NEC 2005. I was thinking of running a 60 amp sub panel as this should more than meet my...

Grounds to be used for shop sub panel [ 4 Answers ]

Have metal pole building about 80 feet from house. I intend to run 100 amp from house panel to sub panel in shop. Originally purchased a cutler hammer mail lug panel CH8L125SP for this use (on sale) but think I would rather have a 100 amp main breaker panel so as to use as single disconnect in...

Installing a 60 AMP sub panel for a work shop [ 1 Answers ]

I have a 200 AMP main panel for my residence with all the breaker slots filled. I plan on removing 2 20 amp breakers and installing a 1 60 x 2 20 amp consolidated breaker in to the panel. Well at least I am told I can do this. I plan on having 2 240 VAC 30 amp breakers in the shop (one will have...


View more questions Search