    Wire size
    The disconnect switch under the electrical meter has a 125 amp breaker, the panel in the home has a 100 amp main breaker. It is an underground service at approximately 50'. Do I size the wire for the 125 amp rating or 100 amp rating?

    Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 20, 2009, 03:35 PM
    125 Amp
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 20, 2009, 03:37 PM

    The breaker cannot be reated higher than the wire, breaker is to be the weak link, would size for 125 amps.
    jjones1941's Avatar
    jjones1941 Posts: 10, Reputation: 1
    New Member
     
    #4

    May 20, 2009, 03:45 PM

    Thanks for the quick response. I know that there are tap rules, but didn't know if this applied.

    Thanks again.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    May 20, 2009, 04:37 PM
    Tap rules?

    Tap rules are only 10 and 25 foot with very, very, did I say very, specific purposes, the longest is 35 feet for an industrial plant. Taps are allowances for using smaller wire fed by a much larger breaker to a smaller breaker very close downstream in the circuit.

    There are other very somewhat rare, specific reasons a smaller wire can be protected by a larger breaker for large motor or refrigeration loads.

    Yours is not any of these.

    You have a feeder. The wire needs to be rated to the overcurrent protection device upstream.
    jjones1941's Avatar
    jjones1941 Posts: 10, Reputation: 1
    New Member
     
    #6

    May 20, 2009, 05:20 PM

    Ok, Thanks again.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    May 20, 2009, 05:27 PM

    If ever in doubt, go the larger size wire to reduce voltage drop, opposed to getting away with the smallest you can get by with. Code was written for safety, not necessarily what is best or most efficient. There are some things code says I can do, but choose other methods that still comply with code.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

Vintage stove- 3 wire 220v, what size wire? [ 1 Answers ]

We recently purchased a vintage Crosley range. The old wire was a 3-wire 220v, connected to terminals in the back- the black and red wires were actually 6 or so copper strands, and the white was a silver metal. My question is, what amperage do you think I need? Will 10 be enough? Thanks for your...

Wire Size and panel size [ 6 Answers ]

I have a separate small living quarters that is a single room that is about 180 feet away from the main panel. It is going to get another little bed room a small kitchen and a bathroom also maybe a washer. The main panel is a 100 amp meter socket combo. What should I upsize the main panel to? ...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search