Eletrical & lighting
How do you wire a series of outlets that can be shut off ( as an emergency ) with the switc of a swith or a push of a button ( DEAD MAN SWITCH )
|
|
 |
Uber Member
|
|
May 14, 2009, 03:55 PM
|
|
If that serious, You could actually have a push or pull switch at each outlet, so when any are pressed, all will be disconnected.
Hopefully HKstroud will see this, he does drawings regularly. My scanner is down, wold have to draw out and take a picture. Will do tomorrow if one not provided by then.
|
|
 |
Electrical & Lighting Expert
|
|
May 14, 2009, 07:04 PM
|
|
You would just wire a typical switch in series with the hot in a box before the receptacles. Then just wire the receptacles as you normally would.
|
|
 |
Home Improvement & Construction Expert
|
|
May 14, 2009, 08:06 PM
|
|
If I understand this question correctly it is "How do I wire an emergency cut off switch for a series of outlets"?
Basically this would be wired like any other switched outlet. The switch could be a toggle switch with an "On and an Off". It could be an Push type switch that is normally "ON", that is the contact points are normally close and "Off" when pushed. A "Panic" button. Either way the switch should be rated for the maximum amperage of the circuit. Wiring would be the same for either switch. If you have difficulty locating a "Panic" type switch you might look at after market cut off switch for table saws. There are several that are designed to be cut off by bumping with your knee. These should also be rated at 20 or more amps.
|
|
 |
Full Member
|
|
May 14, 2009, 09:37 PM
|
|
Don't forget to make sure the switch is rated for the amps that the circuit may be pulling under a full load. Get a heavy duty switch if possible. If you require a smaller light duty switch, you may want to inplement a contactor.
|
|
 |
Full Member
|
|
May 15, 2009, 01:27 AM
|
|
What is the application? Is this for a residence?
When you say "Deadman's" switch, I am assuming you mean momentary contact pushbutton.
This requires an industrial type 3-wire start/stop circuit with a relay that is rated for the load, or a push/pull button like you see as an emergency shut-off for the gas pumps at the 7-Eleven.
You could do it, but it is more cost efficient to simply switch the receptacles off with a toggle. If this is a home installation, you would have an easier time getting it past the electrical inspector.
|
|
 |
Uber Member
|
|
May 15, 2009, 04:32 AM
|
|
HK, can you provide a drawing with his "deadmans" next to each receptacle, that will shut off supply to all recepticles for poster? Thanks
|
|
 |
Full Member
|
|
May 15, 2009, 10:58 AM
|
|
 Originally Posted by Stratmando
HK, can you provide a drawing with his "deadmans" next to each recepticle, that will shut off supply to all recepticles for poster? Thanks
My scanner isn't working either. Must be sunspot activity. What you are describing is an "EPO" circuit that is used in computer rooms. There are usually EPO pushbuttons at each exit which drop out all power to the room. Many industrial applications have "E-Stop's" at places where someone could get tangled up in machinery.
This is basically a 3-wire motor start/stop circuit, with multiple stop buttons. Instead of a motor starter, you are pulling in a contactor to control the receptacles. (In a computer room, the circuit is usually connected to a UV trip on the main circuit breaker) Here is a link to a motor control page. Figure 3 shows the circuit. I couldn't find one with multiple stops, but you wire all the stop buttons in series. In an EPO circuit, the "Start" button is usually a key switch. All the switches are momentary contact.
Please note this circuit will also drop out on power loss.
http://http://ecmweb.com/training/electrical_basics/electric_ladder_logic_basics/
Which beggers the question, why go through all this when a simple switch will drop out power to all the receptacles. I have a feeling this is not a residential application, and the OP should get a qualified contractor to install the circuit.
|
|
 |
Uber Member
|
|
May 15, 2009, 02:43 PM
|
|
I was thinking of Single pole switch, with Push to open circuit, normally they would all be out in the closed condition.
None would be momentary, all would be in series with power to the recepticles.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Rules regarding Eletrical panel
[ 1 Answers ]
Hi everyone I have just joined this group. Thank you in advance for your time in reading this. My husband and I are now renovating our basement and would like to make a laundry room/ bathroom to help with the kids growing up and needing more space. But we are continually getting mix info regarding...
Eletrical and lighting
[ 2 Answers ]
I have a Hampton Bay track light I took from my previous home and I want to install it above my sink in the kitchen of my new home. The track the lights slide into is too long to fit in the area. Can you cut the track to shorten it or are the electrical units inside this unit?
Eletrical outlet
[ 4 Answers ]
Hi,
I have a problem. My problem is that my TV, dvd, and surround sound all hooked up to one outlet in the living room. All of them shut on and off at the same time. I checked the breaker and it is not tripped. I changed the TV, dvd, and surround sound to a differ outlets and the problem still...
Faulty eletrical work
[ 3 Answers ]
I recently had some electrical wall outlets installed in my home but since the install my TV,my stereo and my theatere system has stop working could these new outlets be the problem
View more questions
Search
|