Ask Experts Questions for FREE Help !
Ask
    sheridjohnson's Avatar
    sheridjohnson Posts: 7, Reputation: 1
    New Member
     
    #1

    May 12, 2009, 08:11 PM
    Hunter 44260 Wiring
    Replacing Thermostat from a iNVENSYS 9420 to the Hunter 44260. I have 7 wires coming from the wall. Tan, Red, Orange, Green, Blue, White, Yellow

    The old had L,C,R (Tan to C, Red to R) Y2, Y1,E,W2,G,O,B (Yellow to Y1, Orange to O, Green to G, Blue to B, and White to W2)

    The New Hunter has G, Rc, Rh, Y/O, W/B, and Y1. I hooked it up and it seemingly worked however I hear a sound like water running and cold air from the area of the filter is when the unit reaches selected temperature and fan off until the fan starts again. I have it wired Green to G, Red to Rc, Tan to Rh, Yellow to Y, White to B and Y1 not connected. Orange and Blue are taped off. I now feel this is wrong. Please help me. Thank you so much in advance. Your friend Sheri
    sheridjohnson's Avatar
    sheridjohnson Posts: 7, Reputation: 1
    New Member
     
    #2

    May 12, 2009, 09:12 PM

    I have been reading other posts and realize it may be helpful if I tell you I have a Rheem Model # RBHA 17J11NFGAI and it is check marked Heat Pump
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    May 12, 2009, 09:14 PM

    Is the new stat you have rated for 2 heat?
    sheridjohnson's Avatar
    sheridjohnson Posts: 7, Reputation: 1
    New Member
     
    #4

    May 13, 2009, 04:43 AM
    The new one if for use with a heat pump. There are 3 switches on the inside of the panel they are Auto Recovery (enable/disable I have it set as enable) System Selector (STD/HP I have it set on HP) and HG/HE (I have selected HE)

    Hope this helps

    Also I have a Rheem Model RBHA 17J11NFGAI heater/ac inside with a Rheem Model # RPLA 030JAZ airconditioning unit/heat pump outside. Hope this helps thanks again -Sheri

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Honeywell t87r1475 wiring to a hunter 44260 [ 4 Answers ]

I have a blue green red orange yellow and white wire from the wall... to a hunter 44620 with the following wiring codes... G RC RH Y/O W/B Y1 Can anyone tell me which wires go to which terminals... there is also a red jumper wire on the new unit... should this be removed..

Hunter 44260 Wiring [ 8 Answers ]

Ok. So I changed my thermostat over the summer to a Hunter 44260 Programmable Thermostat. Had no problems over the summer using the AC. Now it's getting a little chilly and the heater will not turn on. When I switch the heater on, the AC condenser turns on but nothing is coming out of the vents...

Replacing a Nordyne Thermostat for a Hunter 44260 Wiring! [ 4 Answers ]

I'm having issues, I want to replace my old thermostat for this digital one however, I'm not sure on the wiring. On the Nordyn I had, Y G R O


View more questions Search