    shylok's Avatar
    shylok Posts: 3, Reputation: 1
    New Member
     
    #1

    Sep 27, 2006, 09:15 AM
    Draining 2tubs 1 shower into 1 1/2
    I'm renovating my bathrooms in my apartment condo unit. Both of them back on to each other with a wet wall between. Everything drains into a 4" stacks and the problem I'm having is that I want to drain

    2 tubs. And 1 shower. Except the T off the 4inch stack is a 1 1/2inch threaded cast iron with copper into it. And then there's two traps for the current two tubs. I want to add a separate stand up shower. But the condo will only allow things done to code. And code says you cannot drain 3into a 1 1/2pipe.

    I'd like to know if I have any options. I was thinking I could raise the tub on a platform and drain into the same 3'' the backflush toilet drains into. But one plumber says that's a nono by code.


    The problem with swapping out the 4'' with the 1 1/2'' T is that part of that T is buried in concrete slab. Probably a full 3inches of that T is.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Sep 27, 2006, 04:18 PM
    " I was thinking i could raise the tub on a platform and drain into the same 3'' the backflush toilet drains into. but one plumber says thats a nono by code."
    By backflush toilet are you referring to a wall hung blow-out toilet? If you vent the shower you could probably get around code restrictions. However,you're talking mjajor surgery here. In addation to getting the Condo Associations approval you're going to hafta decide if the showers worth the hassle. Good luck, Tom
    shylok's Avatar
    shylok Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 27, 2006, 04:53 PM
    Toilet is sort of like that. It's not wall hung mind you. But same idea. It's back outlet/back flush. So it's drain is horizontal into the 4'' stack. Everything is overly vented more than what's required i.e.. 1.5inch venting etc.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Sep 28, 2006, 06:52 AM
    You're still going to have to vent the shower. You can not install the shower downstream of the toilet without a vent. Regards, om
    shylok's Avatar
    shylok Posts: 3, Reputation: 1
    New Member
     
    #5

    Sep 28, 2006, 04:31 PM
    http://www.terrylove.com/forums/showthread.php?t=8824

    Here take a look if you don't mind. I've posted some pictures. I'd like to drain that shower into one of the traps that are there. (which is currently for a bathtub) and I'd like to drain the tub placed on a platform into that 3" which would be extended to get a fitting in there to allow it.
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #6

    Sep 30, 2006, 09:53 AM
    Can you chip out enough concrete to remove the 4"x1"-1/2 sanitary tee?

    If you can, and decide to do so, bear in mind that doing so will change the elevation of the closet flange -- Which will mean building up the bathroom floor and altering the W/C vent enough to make up the difference.

    Just my two pence.
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #7

    Sep 30, 2006, 10:59 AM
    I had another thought, but you're probably not going to like it, because it would mean greater expense and some slight changes in your original design.

    You could go with a Zurn back to back carrier connected to the 3" sanitary tee -- This would scoot the toilets a little closer to the tubs, which will be fine so long as you have 15" of clearance from the center of the toilet to the edge of the tub -- And from your pictures, side clearance doesn't seem to be a concern.

    If you go with the Z1203-ND3 carrier, you'll have an extra 3" outlet aimed towards the lavatories, which can be bushed down to 2" and used to pick up the lavatories.

    The other 3" sanitary tee picking up the other toilet can be removed and bushed down to 2" and used to pick up the new shower.

    The nicest think I can say about this lay-out is you won't have to futz around with the fitting picking up the tubs.

    Some drawbacks:

    The carrier isn't going to be cheap.

    The wall hung toilets aren't going to be cheap -- Or readily available.

    The shower will definitely have to be built up.

    Your plumbing walls will have to be adjusted to accommodate the carrier.

    Depending on the elevation of the 4"x3" sanitary tee picking up the Zurn carrier, the toilet heights may not be optimum.

    Adding the shower might be problematic if all you have available is the existing 2" vent for both baths.

    There is another solution of course, but this depends on ceiling heights.

    You could build both bathrooms up a foot and a half, build steps and have plenty of room for a bath with conventional fixtures.

    Just my two pence.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My dishwasher is not draining [ 2 Answers ]

I just installed a new disposal. Now, when I run the dishwasher it doesn't drain. But if I disconnect the hose from the washer to the disposal and let it run into a bucket it does drain. I don't know what I did when switching the old disposal to the new one but apparently I missed something.

Draining shower causing bubbling toilet [ 1 Answers ]

My basement shower/bathtub, when draining, is resulting in bubbing in the toilet next to it! Would the obvious answer be due to hair clogging the shower drain or would it be further down the line leaving the house? What are a few home rememdies I could do before getting a snake or plumber?

Trouble with washer draining. [ 1 Answers ]

I live in the city. I noticed that when I wash clothes that the drain water comes up in the bathroom tub and also the toilets. Is there anything that I can do to fix this? Can I use some draino or something in the washer drain? Thank you...

Toilet not draining [ 3 Answers ]

We have just installed two 2-piece toilets. We have an intermittent but regular problem with flushing the toilet where upon flushing you hear/see an airbubble and then the toilets fills with water but the swirling action is only half hearted and the toilet doesn't drain away. A second or third...

Tub is the only system not draining properly [ 3 Answers ]

Our house is an older house (ca. 1955) on a septic system. We bought the house and moved in back in late March of this year, when the septic system should have been pumped by the previous owners. We're currently having issues with our bathtub not draining properly. All of our other drains are...


View more questions Search