    Wiring Gage Importance
    Does Wire Gage have that much importance when going from the line source of 14 gage, to the load source at 12 gage.
    Perito's Avatar
    Perito Posts: 3,139, Reputation: 150
    Ultra Member
     
    #2

    May 10, 2009, 12:59 PM

    Under the National Electric Code, the wire size determines the maximum current-carrying capacity of the circuit. 12-gauge wire in households is normally allowed to carry up to 20 amps. 14-gauge wire under similar conditions is normally allowed to carry only 15 amps.

    Wire always has a resistance. As current passes through the wire, some power is dissipated as heat . This is accompanied by a loss of voltage. If you have very long runs of 14-gauge wire, the voltage drop will be greater than the same run of 12-gauge wire.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    May 10, 2009, 03:51 PM
    Quote Originally Posted by electromack View Post
    Does Wire Gage have that much importance when going from the line source of 14 gage, to the load source at 12 gage.
    To be honest I have no idea what you are actually asking, but YES, wire gauge does matter.

    The circuit must be fused/breakered for the smallest wire in the circuit. So mixing wire sizes makes absolutely no sense. In some cases it would create a violation, such as a kitchen receptacle circuit that is required to be a 20A circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Proper wire gage [ 1 Answers ]

Currently my sub panel in the garage is supplied by 10 gage 2 wire with ground from a 30 amp dbl pull breaker in the house. The run is 30' to the 100 amp box in the garage. The garage is a part time workshop with several power tools on at the same time along with 10 4' fluorescent light fixtures...

12 Gage wire 110 outlet [ 1 Answers ]

What amp breaker should I use for a out side 110 outlet using 12 gage wire.Used for plugging in vacuum cleaner to clean cars.

12 gage wire on a 15 amp switch [ 1 Answers ]

If you can use 15 amp receptacles and switches on a 20 amp circuit, then why won't they accept (quick connect) 12 gage wiring?

Water pressure gage reading [ 3 Answers ]

I live in a townhouse with city water. My water pressure gage was reading 225 psi which had been rising for the past two years. Two days ago one of my overhead sprinklers started leaking so had to have it repaired. Two years ago another sprinkler pipe got a pinhole leak in it. The repairman said...


View more questions Search