    Grounding Rod-Detached garage
    Reading other responses to wiring detached garage, most replies suggest grounding rod, in addition to the ground wire that is from the Main panel. My garage sub-panel does not have a grounding rod, I would like to get some information on installing one. Is there a minimum distance from the main panel grounding rod to the sub-panel grounding rod? Do I just drive the new rod into the ground and attach it to the ground bar, that is, by the way, isolated from the neutral bar, in the sub-panel? Thanks for your help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 9, 2009, 03:12 AM
    Any two ground rods must be at least 6 feet away from each other.

    Simply drive the rod, and connect to the equipment ground bar using min of #6 copper wire. All 8 feet must be in the ground, use a ground rod wire connector that is rated for direct burial.

    Why does it sound like the rod existing for the main service will be close to the rod for the garage panel?
    electromechanic's Avatar
    electromechanic Posts: 26, Reputation: 1
    New Member
     
    #3

    May 9, 2009, 11:07 AM

    I either heard or read there was a minimum distance, but could not remember. The two rods will be near 60' apart.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a detached garage [ 5 Answers ]

I am building a detached garage 300' feet from my home and main breaker panels. The meter is out by the road right of way 450' from the home. The garage is going to sit somewhere in the middle about 150' down the hill. Rather than tap into the house panel I'd like to come right off the meter at the...

Detached garage wiring [ 4 Answers ]

Built a detached garage in backyard, the underground line only allowed for 6-3 wiring. The 6-3 had to travel 110 feet to get to the sub panel in the garage. The garage is an 800 sq ft garage with a loft above it. The loft will eventually be converted into a small apartment. I plan on having a...

Detached garage pad [ 2 Answers ]

I am trying to get some information on building a garage starting with the Pad. I am planning on building a 22X26 detached garage. The rough grade was completed about 4 months ago. It is a clay base with no topsoil added yet. Should I get a bobcat in to remove a couple inches or just pack down...

Detached garage grounding rod or not [ 1 Answers ]

Hi, I just ran across another problem. I will be running 40 amps 240 volts out to my garage via underground 8-3 plus ground. Do I need a grounding rod at the garage or is the ground via the service cable to the garage enough? I have seen both and am not sure why. Is the 240 volt service to the...


View more questions Search