    Breaker Panel with No Ground Bar
    Older triplex built in the 1960's, sub panel has no ground bar. Would like to install a dedicated 20 amp breaker and run new wires, what happens to the ground wire if there is no ground bar in the panel to connect too? Would it be OK to leave ground wire caped and just have the neutral and hot connected only? This is how it is done with rest of the outlets, no ground wire.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 6, 2009, 03:14 PM
    Quote Originally Posted by slimjim43 View Post
    Would it be ok to leave ground wire caped and just have the neutral and hot connected only? This is how it is done with rest of the outlets, no ground wire.
    NO! The existing receptacles are 50 years old. Codes have changed just a bit since they were installed.

    Is this a main breaker panel, or is there a main disconnect ahead of it?
    slimjim43's Avatar
    slimjim43 Posts: 5, Reputation: 1
    New Member
     
    #3

    May 6, 2009, 04:21 PM
    This is a sub panel. The main shut-off is outside. I like to install a 20amp and run Romex 12/2 wire to hard wire to an AC, what do I do with the ground wire since there is only a neutral bar. Since today code require a ground, does that mean I have to replace the breaker box with a new one? Any other options?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 6, 2009, 05:34 PM
    There should be a ground bar in that panel. The only way it is possibly legal is if everything is in conduit and the conduits are the grounds for everything.

    IF this is the case you can add a ground bar right to the back of the panel. If you do, make sure it is the same brand as the panel and you use machine thread screws to install it.
    slimjim43's Avatar
    slimjim43 Posts: 5, Reputation: 1
    New Member
     
    #5

    May 11, 2009, 08:22 AM
    I have attached a picture of the sub panel. There is only the neutral bar on the right hand side. I do not see a ground bar.
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Sub-panel needs ground rod? [ 1 Answers ]

Is that true? It seems odd that I would have to drive a ground rod for a 100A subpanel in my detached garage when if I were to install a 100A sub panel right next to my original panel (for more circuits) I would'nt be required to drive another ground rod.

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Ground bar in sub panel [ 1 Answers ]

Hi, I want to wire a 240 Volt sub panel in my garage and I have the 2 live wires, the neutral and a ground wire coming in . In the sub panel, there is a insulated neutral bar and the 2 connectors for the live wires. There is a little piece of metal with an instruction for grounding which...


View more questions Search