    Do I need to carry the Ground Wire
    I have a 200 amp service pedestal which is properly grounded using the 2 ground rods and copper wire spaced 8 feet apart. I want to add an RV pedestal about a hundred feet away and plan on using #6 THHN in conduit with a 50 amp breaker. In addition, I will be putting in a separate service to my well from the pedestal on a separate circuit and it also, is about 150 feet away from the pedestal. Both panels are approved outdoor panels. My question is this. Am I required to run the 4th (Ground) conductor between the pedestal and the well panel and how about the RV panel? Can I use additional ground rods at each of the new panels instead. I get confused on when to use the 4th wire and when not to run it. Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 5, 2009, 08:42 AM
    Yes, the fourth wire, the equipment grounding conductor, must be run with any branch circuit or feeder after leaving the Main panel or disconnect.

    The neutral must remain insulated and isolated from the EGC. The EGC will connect to a equipment ground bar in the pedestal or subpanel. This bar may need to be purchased separately as an accessory.

    Ground rods cannot be used in place of the equipment grounding conductor.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #3

    May 5, 2009, 08:52 AM

    Thanks for the quick reply. I will run the 4th wire. I had already purchased the separate grounding kit for the sub panel and the RV Panel already came with it installed. Only problem was that I had installed grounding rods as well and used bare copper to connect to that panel bar. Can I use #8 THHN for this 4th wire? 50 amp breaker on #6 THHN Wires. Thank You again.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 5, 2009, 09:09 AM
    Yes, the #8 will be fine as an EGC with the branch circuit. And #6 THHN/THWN, (be sure the wire is THWN, as most THHN is dual rated), is fine.

    As far as the ground rod for a remote panel...

    If the remote panel was IN or Serves a building or structure, a rod is required.

    I am not sure,and I did check if one is needed for the pedestal, and could not see that one is needed.

    One is not needed for the well, being a single branch circuit. Keep in mind, the well casing makes a hell of a ground rod.
    Bowler's Avatar
    Bowler Posts: 133, Reputation: 2
    Junior Member
     
    #5

    May 5, 2009, 09:28 AM

    Just so I am clear on this... The RV panel is situated by inself and is mountes on a treated 4x4 and will require the 4th wire and no ground rods. Correct?

    The well sub panel is located outside and not in a building. It is "New" work and it also will require the 4th wire and no ground rods. From the branch circuit breaker from the Well sub panel to the pump starter, of course will be connected to the sub panel ground. Correct?


    The main 200 amp Pedestal Service panel already has #6 bare copper connected to the 2 ea ground rod rods that are 8 feet apart
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    May 5, 2009, 10:21 AM
    Correct on both items.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Misuse of ground wire as neutral return wire in old house [ 5 Answers ]

Here a problem where the "obvious" solution scares me, need some advice on how to best proceed. My home (built 1920 with knob and tube type wiring) has been upgraded over the years by prior owners, but in many place still has active current in the old wires, in other places it is spliced into a...

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

10/2 wire to carry 220 v - panel attachment [ 4 Answers ]

The HVAC guy will install the AC but I need to get 220 v to the compressor. The house was wired when it was built and I have a 10/2 wire running from the panel to a box in the furnace room. The black is loose in the panel and the white is attached to a common. The panel has one open spot but I...

Can you use Metal Conduit as ground to convert 2 wire to 3 wire? [ 3 Answers ]

I need to convert an old cinder block house from 2 wire outlets to 3 wire by adding a ground to all outlets. Since the entire house is cinder block, all the circuits from the basement breaker box are in flexible metal conduit and metal outlet boxes... Is it possible to use the metal conduit...

Armored cable carry two sets of wire for two circuits? [ 27 Answers ]

Strange question. I opened up my fuse panel box to see which fuse was for what circuits as its really old and although it was labeled, it wasn't completely labeled. Fuse 1 and fuse 3 hots, go into the same armored cable it seems. And this isn't the neutral either, as the neutrals go to a bus bar....


View more questions Search