    May 2, 2009, 02:34 PM
    GMS8 blows fuses when on A/C
    I've got a Goodman GMS8 A/C and furnace and the problem started a few days ago where:

    - the thermostat has no temp reading
    - no response when the thermostat is cycled from off to cool or warm (with either set to auto or on)
    - no response when I reset power on the circuit breaker
    - checked on the LED status light and it's off inside the unit
    - checked the controller board and the fuse was blown
    - replaced the 3A fuse and it blew again
    - replaced the fuse again and I had the thermostat set to OFF (temp) and ON (fan) before I powered it on from the door switch
    - the blower comes to life then I asked my helper to switch it from OFF to COOL and it blew the fuse
    - checked for any loose or possible short on wires, nothing too apparent. I plan to double check it again today

    Any other ideas on what I can do?

    Thanks in advance.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 2, 2009, 03:57 PM

    Your contactor outside in the ac is probably bad. Take the t-stat wires loose from the outdoor unit then try it again see if the fuse blowes
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #3

    May 2, 2009, 09:04 PM
    Check for low voltage shorts on the thermostat wire from the thermostat to the furnace and to the A/C and check for shorts on the low voltage side at the A/C(low and high pressure switch, time delays).
    ramond's Avatar
    ramond Posts: 3, Reputation: 1
    New Member
     
    #4

    May 4, 2009, 02:16 PM
    Quote Originally Posted by Joshdta View Post
    Your contactor outside in the ac is probally bad. Take the t-stat wires loose from the outdoor unit then try it again see if the fuse blowes
    Thanks for the response. I just want to understand this. If I remove the t-stat wires from the outside unit and the fuse does not blow, it's the contactor that's the issue. If the fuse blows while the t-stat wires are disconnected, then it would be a short on the t-stat line? Right?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    May 4, 2009, 03:43 PM

    Correct, odds are the contactor is your problem, inless you hit the t-stat wire while weed eating. Contactors run about $25 and are easy to replace.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    May 4, 2009, 03:46 PM

    Please let us know what you find.
    ramond's Avatar
    ramond Posts: 3, Reputation: 1
    New Member
     
    #7

    May 12, 2009, 05:32 PM
    Quote Originally Posted by Joshdta View Post
    Correct, odds are the contactor is your problem, inless you hit the t-stat wire while weed eating. Contactors run about $25 and are easy to replace.
    After so many rainy days, I finally got out and checked the t-stat lines. The fuse doesn't blow when they're not connected. So I ordered a replacement contactor and replaced it today. I've got A/C back!! Thanks for all the help.

    :D:D:D:D
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #8

    May 12, 2009, 06:09 PM

    Great, glad you got it going!! Job well done.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman heat pump does not switch on for heat and the AC blows A/H fuses. [ 4 Answers ]

My Goodman heat pump, model GSH130361AD, heat does not switch on (outer unit). When it first went out, the Honeywell T8411R t-stat digital display went blank. First, I tried replacing the stat with other, but they only accommodated 5 wires. Wiring to the Honeywell was 7 wires. I'll come back to...

Why John Deere 2148 Sabre blows fuses? [ 1 Answers ]

For about a month, it would blow the 15 A fuse in the starter circuit after being run for a while, shutting it off briefly, and then starting it again. It usually only blew after being shut off 6 or more times. Gradually, it blew sooner, and now it blows the first time I try to start it. ...

Circuit board problems with gms8 [ 2 Answers ]

Is there a history of problems with this circuit board in the gms 8 furnace?

Craftsman riding lawn mower blows fuses [ 6 Answers ]

I have a 03 Craftsman 15.5 hp riding lawn mower. The 30amp fuse between the solenoid and ignition switch keeps blowing when I try to start it. I changed the solenoid and the fuse. My battery was low so I used an extra car battery to jump it. I turned the key and heard the fuse pop. I suspect the...

17 1/2 hp mtd blows fuses [ 3 Answers ]

Hi, my dad has an mtd 17 1/2 hp gear drive mower, just after he bought it, it started blowing the fuse. Warrentee took care of that one. That was six years ago, now its blowing fuses again. Replaced the fuse again, but then I installed wire loom on every wire I could get my hands on. The wires...


View more questions Search