    Ducane Heat Pump-Outside Unit not coming on
    I am having constant problems with my Ducane heat pump. For the last few months the outside unit might come on and it might not--does this on both heat and cooling. Over the past few weeks it seemed to be working better then last week it quit coming on again--in fact now the only way to get it to come on is to reset the main breaker on the house and then it would work the rest of day until yeterday... yesterday it wouldn't come on, so I flipped the breaker, then turned the air on and the outside unit ran for 3-5 minutes and quit. I flipped the breaker again... same result... any idea?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 29, 2009, 02:01 PM

    Does the whole thing quit, or is it just the compressor, or the fan outside that shuts off? Or does everything shut down at once like there is no power?
    buckeyeluvngirl's Avatar
    buckeyeluvngirl Posts: 4, Reputation: 1
    New Member
     
    #3

    Apr 30, 2009, 04:59 AM
    The fan outside quits. I took the panel on the inside unit off last night and watched it very closely--here is exactly what happens:

    -Turn the thermostat to cool and set temp--the therm click once and the fan on inside unit comes on. 2 or 3 minutes later the therm clicks again and outside unit normally comes on--nothing happens.

    -Go to garage and flip main breaker off and back on--go back to thermostat--switch to off and then back to cool. The therm clicks and fan on the inside unit comes on-2-3 minutes therm clicks again and outside unit comes on.

    -Go to garage and look at inside unit--A-Coil--the copper tubing on the very bottom (it does not spread any higher than the bottom row of the copper but it happens on both sides amd also covers the really thin copper tubing that comes from outside to the a-coil) starts to get a thin layer of frost on it like it is freezing up. After about 30 seconds the ice/frost completely disappears.

    -Go outside and the outside unit is not on anymore.

    Thank you for your time!
    buckeyeluvngirl's Avatar
    buckeyeluvngirl Posts: 4, Reputation: 1
    New Member
     
    #4

    Apr 30, 2009, 05:09 AM
    When the ice/frost disappears and I go outside to the outside unit--the inside unit fan is still blowing and will continue to blow until I switch the therm to off or adjust the temp high enough to make it turn off.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    Apr 30, 2009, 05:21 AM

    Sounds like you may be low on freon and your unit might have a low pressure lockout. Ice will build on the insiide from lack of charge with freon, or low air flow. How is your air filter?
    buckeyeluvngirl's Avatar
    buckeyeluvngirl Posts: 4, Reputation: 1
    New Member
     
    #6

    May 1, 2009, 05:09 AM
    Air filter is clean. Finally broke down and called a repair guy. He added some freon and that fixed the problem till this morning it is doing it again. Called again and he said checked for leaks yesterday and couldn't find any--said leak most likely in A-Coil and be best to just replace the whole unit. I have read a lot of talk about inside and outside units not matching--mine doesn't--my oustide is a Ducane and my inside is a janitol-which looks kind of older. He said this also could be causing me a big problem--it is a split level house that I have lived in for almost a year-during the summer last year the upstairs never dropped below 75 degree and the air ran constantly--I also had the freon checked and added last summer. Do you think the repair guy is on track or just looking for a sale? Also, will I have to replace the outside and inside unit both to get a matching set? The outside unit appears to only be a few years old.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    May 1, 2009, 05:25 AM

    Well, that depends on if a few yrs old means older then 3 yrs? 3 yrs ago the government made us change the efficiency of the units so you may have to get both to work right. Also if he charged it right there is no way that it should have leaked out that fast. If it did then he should be able to find that leak. Also ducane heatpumps are famous for leaking at the low pressure control outside. You can put some liquid soap on it and see if it is where it is leaking. All you need is 2 crescent wrenches to tighten it up.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I connect new outside unit to older inside unit for a heat pump? [ 2 Answers ]

I have a heatpump system. The outside unit is very old and is different manufacturer than the newer (9yr old) inside unit. Outside unit has gone bad. Can I connect a new TRANE Outside unit with SEER of 13 to my 9 year old TRANE inside unit with SEER of 10 which still seems to be working...

Heat pump auxiliary heat keeps coming on. [ 13 Answers ]

One of our 2 Ruud heat pump keeps cycling on auxiliary heat. The installer says there is nothing wrong, if so why is the other one working properly, plus in the summer it will not get below 76 degrees with that same unit. Freon is fine.

Rheem-heat-pump-outside-unit-humming but blower unit working [ 3 Answers ]

I have a heat pump and ac unit outside. The inside blower fan still working but the outside unit humming. Are there any quick fixes here

Thoughts of a ducane heat pump 3 ton [ 1 Answers ]

I would like to get a few oppinions of a ducane heat pump? I have already bought a 3 ton unit, I hope I done OK?

RUUD Heat Pump Outside Unit Fan not coming on [ 1 Answers ]

I just closed on my house - made one payment and the outside heat pump is not working!! About 3-4 weeks ago the fan on the outdside unit just sounded a little rough, almost a slight grind/knocking noise- although nothing major or too out of the ordinary for a fan motor ,just a little bit...


View more questions Search