    Apr 26, 2009, 08:40 AM
    Outside unit does not shut off
    We turned our a/c on yesterday for the first time. We didn't notice anything out of the ordinary until several hours later when we adjusted the thermostat to force it to stop running. The outside unit continued to run even after I set the thermostat to off. The copper tubing leading into the blower unit in our basement was extremely cold with frost on it. After several more hours of it running for no reason, I had to shut the circuit breaker off in order to stop it. My outside unit is a Jantrol?? presumably the original unit when the house was built in 1988. Any ideas??

    Thanks,
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Apr 26, 2009, 08:52 AM

    I would check for power to coil on outside contactor for 24 volts, if none is present and power is on load side of contactor, it may be welded closed. Replace/clean?
    If 24 volts is present at contactor coil, then it is thermostat or control wiring problem.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Apr 26, 2009, 09:20 AM

    I agree you need a new contactor.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC Compressor unit will not shut off [ 2 Answers ]

Here is the problem. Lets say it is 80 degrees. I turn the central air conditioner on, set at 78 degrees. The house cools down to 78 degrees. The thermostat appears to shut the blower (from the furnace) off and acts like it everything is shut off. However, the outdoor AC unit continues to run and...

Central Heating Unit will not shut off [ 1 Answers ]

My wife noticed it getting warm and turned the thermostat down. It was set on heat, 76 degrees, she put it below 60's and the unit kept running. I shut it completely off and it kept running. The only way it shut off was by tripping the breaker. We waited a good hour and when I flipped the breaker...

Heat on central unit will shut down [ 3 Answers ]

Heating syste on central air unit will not shut off t-stat has been replaced. Disconnected power for unit and check relays in system have one relay that is operates fan and another that that routes power to fan really and to heater coil both had continuity until I disconnect power wire coming to...

Outside a'c unit won't shut off [ 2 Answers ]

My A/c Unit Out Side Won't Turn Off When The Thermostat Inside Is Turned Off.there Is Also Ice On The Lines Outside.I Have A Dual A/c System, One For Each Side Of The House. I Turned Off The Main A'c Switch ,the Fan Stopped And I Heard A Click, I Waited 1 Min. And Turned It Back On Again And Heard...

Why my home a/c unit shut off hard [ 2 Answers ]

My home a/c unit shut off with a hard sound.