    Hot Tub wiring
    My hot tub runs on 220. When I turn on both pumps the red wire get hot and melts the cap. The gfi does not trip. Could it be a bad ground or is it miswired?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Apr 25, 2009, 10:13 AM

    I see you are covering your bases by posting this on electric and Spas. You are already getting some great questions on electric, try to answer him. Your pool is more likely 240.
    chemicalfree's Avatar
    chemicalfree Posts: 22, Reputation: 1
    New Member
     
    #3

    Apr 25, 2009, 10:51 AM

    You didn't say what brand hot tub you have, but some things to check:
    1. Check for any loos wiring or screws holding the wiring in place.
    2. As the heater gets older it draws higher amps thus causing more heat. How old is the spa heater?
    3. When all pumps and equipment are on you could be execeeding or approaching the AMP raring of the breaker and if any of your equipment is old (Pumps, heater, blower, etc.) they could be causing the system to work harder, thus causing a build up of heat.
    4. Try first turning the heat down as low as it will go and then run both pumps to see is line heats up. One of your components could be causing the problem.

    God Luck
    tommac407's Avatar
    tommac407 Posts: 8, Reputation: 1
    New Member
     
    #4

    Apr 25, 2009, 10:55 AM
    Quote Originally Posted by chemicalfree View Post
    You didn't say what brand hot tub you have, but some things to check:
    1. Check for any loos wiring or screws holding the wiring in place.
    2. As the heater gets older it draws higher amps thus causing more heat. How old is the spa heater?
    3. When all pumps and equipment are on you could be execeeding or approaching the AMP raring of the breaker and if any of your equipment is old (Pumps, heater, blower, etc.) they could be causing the system to work harder, thus causing a build up of heat.
    4. Try first turning the heat down as low as it will go and then run both pumps to see is line heats up. One of your components could be causing the problem.

    God Luck
    It's a cal spa and its about 15 years old. They only thing I have replaced is one of the pumps. Although it has tripped the breaker if I have both on for long periods. I just want to make sure there is no way someone could get electricuted while in the tub
    chemicalfree's Avatar
    chemicalfree Posts: 22, Reputation: 1
    New Member
     
    #5

    Apr 25, 2009, 01:15 PM

    All tubs should be wired with some type of GFCI or disconnect 5Ft. From the tub or the GFCI might be located in in the main panel box. The purpose of the GFCI is to protect against current leakage to the water, however if your wire are getting hot enough to melt that is evidence that something else is going on with one of the electrical appliance in the tub or one of your connections are loose.

    If you have never replaced the heater take a look around the electrical connection points for the heater on the heater barrel and if you see evidence of rust this means you have some water leakage no matter how slight and this could cause the GFCI to trip or it could even cause the condition you described earlier.

    With the age of the spa the equipment is laboring harder.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring direction for a multi wiring system thermostat! [ 3 Answers ]

I have a 2 wire system (3 phase), need to connect multi wiring system thermostat! Need to know if, its correct to just use line#1, and the device already has a jumper?

Janitrol wiring to rth3100c wiring [ 1 Answers ]

I've taken off the cover and the wires are all OK but the black one where does it go to? My heater won't come on (well some times the AC come on with out me turning it on.)

Honeywell wiring different from old thermostat wiring [ 2 Answers ]

I purchased a non-programmable digital thermostat to replace an analog thermostat with wiring red, white yellow and black. How do I match the wiring? HELP!!

John Deere - My dog ripped the wiring Out - Need Wiring Diagram or photos [ 2 Answers ]

I have a 3 year old L110 that ran fine until last week. I think my dog chased a chipmunk up under the hood and in trying to get to him ripped a bunch of wires out. I have spliced back together the obvious wires (color coded) but I have one black wire that I assume is a ground(?) and the two...


View more questions Search