    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #1

    Apr 24, 2009, 02:51 PM
    Outside fan nor compressor coming on when thermostat requests
    I have about a 10 yr old system, and a programmable thermostat. It's a gas furnace, trane is the brand, I believe it's a 2 ton unit. Also a trane setup outside as well. My thermostat is calling for cooling and the fan in the furnace comes on but the outside unit is doing nothing. I've checked breaker in fuse box and also the one on the side of the house and all power is good. Any ideas? I think I need to check and make sure that the furnace is signaling the ac unit.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 24, 2009, 02:52 PM

    t-stat wire is broken, or contactor or compasitor may be bad
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #3

    Apr 24, 2009, 03:00 PM

    What are you talking about when you say a contactor? I know what the capacitor is, but not a contactor
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Apr 24, 2009, 03:01 PM

    Contactor is inside the electric pannal on the outdoor unit. It will have both the t-stat wires and the main power hooked to it
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Apr 24, 2009, 03:01 PM

    Open the acces panel to electrical on outside unit. You will see a contactor. Some are sealed contacts, most are open. If yours is open, take a screwdriver and manually push the contacts closed. If unit turns on, then you will have to find the break in the thermostat wiring, between furnace and outside condenser unit. Please let us know what you find. And come on back for any further questions.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #6

    Apr 24, 2009, 03:01 PM
    http://yueqing-shi-shinaidi-electric...ges/283101.jpg
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    Apr 24, 2009, 03:02 PM
    Look at the 2 poles in the middle of it and see if they are pulled in.
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #8

    Apr 24, 2009, 03:06 PM

    Now when you say the electrical panel outside, are you talking about the one mounted to the house with the breaker in it, or where the wiring enters the unit?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #9

    Apr 24, 2009, 03:09 PM

    Where the wires enter the unit.
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #10

    Apr 24, 2009, 03:10 PM
    I will do that and report back
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #11

    Apr 24, 2009, 03:25 PM

    OK, I manually pushed the contactor in and the outside unit came on. When I removed the access panel I found a booklet with the model # and such. The condenser unit is a trane model:TTB024C100A0. I have a sneaky suspicion that I have a chewed wire in my basement. Last fall when I turned the furnace on I found the tube for the psi sensor chewed, and had to replace it. So I think I know where to look...
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #12

    Apr 24, 2009, 03:29 PM

    Yep if it runs with the contactor pushed in you have a t-stat wire problem
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #13

    Apr 24, 2009, 03:29 PM

    Doesn't look like my post made it... pushed contacts together and it runs. I had a slight mouse problem last fall when it cooled off. I had to replace the hose for the psi sensor in the furnace last fall. So I think that I am going to need to look in the basement for some chewed wiring.
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #14

    Apr 24, 2009, 03:31 PM

    OK, so I answered twice... now with the tstat commanding ac on according to the display, and its not on, it is definitely a wiring issue between the furnace and condenser unit, right?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #15

    Apr 24, 2009, 03:32 PM

    Yep, you got it, now all you have to do is some searching. Lol sometimes that ends up being the hardest part
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #16

    Apr 24, 2009, 03:33 PM

    Tell me about it... just sucks listening to my "better" half whine about how its 80 inside and the air is on... lol. Ill check in in a little while and tell what I found
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #17

    Apr 24, 2009, 03:34 PM

    I really appreciate the help guys!
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #18

    Apr 24, 2009, 03:37 PM

    OK good luck, I will be back on in a hr or so
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #19

    Apr 24, 2009, 03:39 PM

    No problem, please let us know how you make out. (with the ac, not the better half, lol). I've learned to tune out the whining by just drinking more beer.
    smitty868's Avatar
    smitty868 Posts: 11, Reputation: 1
    New Member
     
    #20

    Apr 24, 2009, 04:22 PM
    Man I totally agree, for that's what I also do. Drinking beer just adds to my selective hearing... lol

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Outside AC condensor/compressor unit not coming on at all [ 7 Answers ]

My outside central AC condensor/compressor unit (a Lennox) is not turning on at all. When I switch on the thermostat, the blower in the basement starts running and air is coming through the vents, but the outside unit is not turning on at all, so there is no cool air. Is the likely problem a...

Compressor and fan not coming on [ 3 Answers ]

I have check wiring at condenser unit out side, compresor and fan will come on and work if you push the button in the center of the relay and hold it but it will go off as soon as you release it.

Nissan A/C compressor not coming on [ 2 Answers ]

I have Nissan 2006 Xterra. There is no output from the IPDM to the compressor. I have already changed the IPDM and the thermal amp behind the glove box but neither worked. Is there an easy way to check the refrigerant pressure switch? Where should I look next?

Lennox compressor not coming on [ 2 Answers ]

HELP PLEASE... I have a Lennox a/c unit... the compressor all of sudden stopped awhile ago. The thermostat display is working fine and the fan comes on when I turn it from "auto" to "fan"... but the outside unit won't come on at all. I tried turning main breaker off and on but nothing. ANY...

AC Compressor and/or thermostat not operating [ 3 Answers ]

I have a Carrier AC-Furnace combination. My wife noticed that our outside air conditioning compressor wasn't operating yesterday. I checked and operated all of the circuit breakers, both inside and outside (by the compressor). However, I noticed that the furnace fan, which blows the air,...


View more questions Search