I think the code says that you need to size a vent at one half the diameter of the largest waste pipe. But I seem to recall somewhere that said a minimum vent through the roof was 3 inches.
|
|
 |
Senior Plumbing Expert
|
|
Apr 22, 2009, 03:12 PM
|
|
Hi Rod...
All houses must, at a minimum, have one 3" vent that penetrates the roof. The minimum vent through a roof, however, is 2".
The minimum vent required for all water closets, whether 3" or 4" pipe is 2"... so here, the 1/2 diameter rule doesn't apply.
Let me know if you have more questions...
MARK
|
|
 |
New Member
|
|
Apr 22, 2009, 03:28 PM
|
|
 Originally Posted by massplumber2008
Hi Rod...
All houses must, at a minimum, have one 3" vent that penetrates the roof. The minimum vent through a roof, however, is 2".
The minimum vent required for all water closets, whether 3" or 4" pipe is 2"...so here, the 1/2 diameter rule doesn't apply.
Let me know if you have more questions...
MARK
What about commercial installation using flush valve water closets? Same rule?
|
|
 |
Senior Plumbing Expert
|
|
Apr 22, 2009, 03:31 PM
|
|
Same rule... 2" vent required for all toilets!
|
|
 |
New Member
|
|
Apr 22, 2009, 04:08 PM
|
|
Awesome, thanks.
|
|
 |
Plumbing Expert
|
|
Apr 22, 2009, 09:34 PM
|
|
They may be combined... and what you see is 3" or 4" vent end piece that penetrates roof. This is more likely in warehouse-type installations where you have several toilets next to each other...
|
|
 |
Eternal Plumber
|
|
Apr 23, 2009, 04:53 AM
|
|
 Originally Posted by RodButler
I think the code says that you need to size a vent at one half the diameter of the largest waste pipe. But I seem to recall somewhere that said a minimum vent thru the roof was 3 inches.
My Code requires one thre inch vent per dwelling, (we put ours in the kitchen) and a 2" vent for every fixture that has a trap with the exception of floor drains.Regards, Tom
|
|
 |
New Member
|
|
Feb 3, 2011, 04:26 PM
|
|
Hi
In British Columbia every building must have one 3" vent.. also any water closet must have min. 1.5" vent and 2" wet vent...and floor drains 3" and larger can vent themselves.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Size of seat valve washer fir water shut off
[ 2 Answers ]
Hi... Hoping someone can help.
When I replaced my whole house water filter today I noticed water was still leaking before I placed the new filter in the container. So I tightened the shut off valve but water still leaked from inside the filter housing. The shut off valve is a 1 inch fitting.
...
Minimum vent size
[ 1 Answers ]
I am installing a full master bath away and inaccessible to the vent stack. I am using a 3" drain(PVC) for toilet, sink and shower. What is the minimum size vent stack I should use?
Up flush bathroom drain and vent
[ 5 Answers ]
Hi all
I am looking at building a basement bath and the drain and vents seem simple, but I am concerned.
I have purchased a saniflow unit
I have raised the floor 7" and will cover it with 5/8 plywood
The room is just over 10x10
There are a few issues that I need help with
View more questions
Search
|