New Member
|
|
Apr 12, 2009, 09:02 AM
|
|
Goodman GMNT Furnace Not Running
I have a Goodman GMNT High-efficiency Condensing Gas Furnace that is not coming on. It is 5+ years old and had been working fine until the last couple of days. Fortunately, weather is getting better (Spring!), so need for heat is low.
It is a horizontal installation, located in the crawl space under the house. It uses a water ejector pump to get rid of the condensate water. I am assuming that the pump is working, but I don't know for sure. There is no sign of water over-flow near the pump or furnace.
I replaced all the air filters, but no joy. Power is on.
I do not hear the vent fan coming on as it normally does before the burners ignite.
New thermostat installed a few months back is working fine.
Any ideas?
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:19 AM
|
|
You say the vent motor is on? Do you see a glow from the ignitor?
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:31 AM
|
|
If the ignitor is not glowing, it could be the ignitor its self or a pressure switch keeping it off. If you take the door off. And the vent motor comes on, and after about 25 seconds you here gas coming into the unit the ignitor is bad. If you do not here any gas the pressure switch is stuck open. There is also a small chance it is the control board not sending power but I will bet it is the ignitor or pressure switch.
|
|
 |
New Member
|
|
Apr 12, 2009, 09:33 AM
|
|
The vent motor is NOT coming on... I would normally be able to hear this before the burners lite. But, no vent fan at present.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:35 AM
|
|
OK on your t-stat switch it to fan on, and see if the blower comes on. This will tell us if anything at all is working.
|
|
 |
New Member
|
|
Apr 12, 2009, 09:50 AM
|
|
OK... the fan works... But, this is the fan that blows air through the duct work.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:52 AM
|
|
OK, well lets see then turn it back to auto
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:54 AM
|
|
When you was in your crawl space did you feel the vent motor to see if it was hot? Also, on that little pump you was talking about there is a main wire on it for electric and probably 2 little blue wires for a safety do you know if the 2 little wires are connected? Also do you have ac on this unit or just heat only?
|
|
 |
New Member
|
|
Apr 12, 2009, 09:55 AM
|
|
Fan is back to Auto...
|
|
 |
New Member
|
|
Apr 12, 2009, 09:58 AM
|
|
This unit is for both heat and A/C.
The wiring to the condensate pump looked OK to me.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 09:59 AM
|
|
If the safety on the pump is wired to the w turmanal on the control board this would lock out the heat from coming on
|
|
 |
New Member
|
|
Apr 12, 2009, 10:00 AM
|
|
I just re-read your question. And, I don't know if the two blue wires on the condensate pump are connect. I would assume so, but I don't know.
|
|
 |
New Member
|
|
Apr 12, 2009, 10:03 AM
|
|
And, this unit has been working great for 5+ years.
However, I am wondering if the condensate line is full. From what little I know about the system, the condensate needs to be ejected or it will prevent the combustion fan from operating, which prevents the combustion process from starting.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 10:04 AM
|
|
OK , does your ac come on? If it does then there should be no problems with that little water pump.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 10:05 AM
|
|
So the next step will be to determine if the vent motor has gone bad or if it is not getting power from the control board.
|
|
 |
New Member
|
|
Apr 12, 2009, 10:07 AM
|
|
Yes... AC seems to work just fine.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 10:07 AM
|
|
If the condesate is full the vent motor fan will still try to run, but with the extra water in it the pressure switch will not make causing the ignitor to not light. Also on the bottom door with the unit turned to the heat setting. There should be a red flashing light. A fault code this will also tell what may be wrong with the unit.
|
|
 |
New Member
|
|
Apr 12, 2009, 10:25 AM
|
|
Sorry it took so long... I had to crawl under the house...
I did not see a flashing light. There is a distinct "buzz", though... an electrical hum. The was from the furnace, not the condensate pump.
The unit is on its side and can not see where the LED might be located and I certainly didn't see anything flashing.
|
|
 |
Ultra Member
|
|
Apr 12, 2009, 10:28 AM
|
|
No problem, OK you should have 2 doors on you unit a upper and a lower. The upper one should be larger and contain the vent moror in in the bottom door is just a bit smaller and will have the control board and the blower motor. This door should have a sight glass on it to see the led light. If not you may have to take the doors off the unit.
|
|
 |
New Member
|
|
Apr 12, 2009, 10:33 AM
|
|
There is an upper and a lower door. Actually, I would call these access panels since they are screwed to the frame.
In the doors there is a hole in which I can look inside. I did that and did not see any LED lights. In the bottom hole, I can easily see the gas valve.
I do not have access to the top, bottom or back of the unit. So, these two panels are the only ones I can work with. Hopefully, the installers put the unit in so that it could be serviced.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Goodman GMNT, noise and blower speed
[ 4 Answers ]
I have a GMNT 120-5, the vent motor is extremely noisy during operations and can be heard in the entire house. Any possibility to repair or should I just replace the motor?
After a recent service call the technicians switched the blower speed to a higher level which due to the high velocity now...
Goodman gmnt-100 won't light
[ 5 Answers ]
My goodman gmnt100 won't light just replaced the ignitor about 3 weeks ago was working fine and then started lighting intermittantly now won't go at all
Goodman Furnace -takes 2 Or 3 Ignition Cycles before Stays Running
[ 2 Answers ]
Hi,hope you can help me out.i have a goodman manufacturing forced air furnace that i believe is giving me a warning sign of a future failure.what has happened is in this order,1st one morning the thermostat showed that the furnace was on and it was'nt.turned it off and then back on at the...
Goodman Furnace won't stay running
[ 3 Answers ]
I have a goodman furnace that won't stay on.. the glow plug comes on and ignites the heat box, it will run then shut off... after it gets to desried heat,, then when you try to get it to run again it's like it shuts down after igniter being lit for about 10 secs, I've replaced batteries in...
Goodman GMNT main switch error
[ 2 Answers ]
It's Easter morning... and it's colder than Christmas morning... and my 5-year new Goodman GMNT furnace is not working. Getting 4 blink code, main / auxiliary switch error. I have turned unit on and off and have it working, however when it shuts down and I think the blower continues to run causing...