    Joining 2 different gauge wires
    I knocked down part of a wall and as a result need to move some outlet wires. I found a good and legal place to put a junction box but the existing wires are stamped 16amp (35yr old house),(I assume that means about a 14ga) and I have 20ga (romex 12/2)---the circuit has a 20amp breaker.
    Can I join these two gauges with no problem or do I need to go get some lighter gauge wire?

    Thanks for the help.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Apr 8, 2009, 06:59 PM

    You can not have 16 amp wire on a 20 amp breaker. You could however drop the breaker down to a new 15 amp breaker. What is on this circuit that would require 20 amps? Most residential baseboard outlets are 15 amp.
    dababooze's Avatar
    dababooze Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 8, 2009, 07:44 PM

    Well, looks like I've got some work then-----I took all the info off the wire itself, checked and rechecked. Guess I got a problem.
    FYI--the circuit includes all the outlets on the bottom floor (townhouse).
    I'm going to have someone come over and check the wiring---thanks for the heads-up.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Apr 9, 2009, 08:33 AM

    I'd actually check the wire diameter and consult the tables to be sure. 16 AMP may have been used long ago, but let's hope it wasn't 16 AWG.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

Re-joining household wires [ 1 Answers ]

A household wire was cut to tap into it to provide current for another fixture. That fixture is no longer needed so I want to rejoin the wires where they were cut. Can I just re-join them with wire nuts and leave it or do they need to be inside a junction box to be up to code? The wire will be...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

Wiring different gauge wires (18 awg to 14 awg) [ 5 Answers ]

I recently bought a house that has a nice wall lamp in the living room that I would like to keep as I renovate it. The lamp came wired with 18 awg wire (1 neutral, 1 hot, and 1 ground). The previous owner wired the lamp to a standard wire with a plug to make it a plug-in fixture. I don't know if...

Joining wires in a junction box [ 1 Answers ]

In wiring a house, I have each room's wiring pulled to a junction box in the attic. Each junction box will be a circuit, with a home run going from the junction box to the panel. There are more wires than a single wire nut can join. Do I use jumpers to group the entire bunch so that that all...


View more questions Search