Ask Experts Questions for FREE Help !
Ask
    rainman5573's Avatar
    rainman5573 Posts: 6, Reputation: 1
    New Member
     
    #1

    Mar 22, 2009, 10:43 AM
    Gas furnace blower does not come on
    My Bryant gas furnace's, (model 376CAV downflow), blower will not come on.
    I removed the front doors and pushed re-set on the draft safeguard tube and the re-set for the manual limit switch. With the doors off, I can hold the blower door safety switch down and the blower comes on (does this mean the fuse is okay?) and the blower runs for a few minutes then turns off, then the burner comes on, but shuts off after a minute or two without the blower ever coming back on. With the doors replaced, the burner always comes on, but never does the blower. I have repeated this procedure several times with the same results. Is there something I can do to remedy the problem without the costly visit of a repairman?

    Short history: flooding caused several heat ducts to fill with water. The water never reached the height of the furnace base, but was within +18". The water has has now receded and is no longer in the crawl space of the house.
    rainman5573's Avatar
    rainman5573 Posts: 6, Reputation: 1
    New Member
     
    #2

    Mar 22, 2009, 10:52 AM

    I should add to my post that the burner always ignites when tripped by the thermostat, but the blower never does come on, without me going through the procedures mentioned in my post.
    rainman5573
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #3

    Mar 22, 2009, 02:07 PM
    Rainman,, its true (life is like a box of chocolates)
    Does it (the led on circuit board ) give a blinking code? If so on the inside of the door/panel you should find something to tell you what the code is

    You could also bypass the tstat bydisconnecting and jumpering the red and white tstat wires and see if you still have the problem
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Mar 22, 2009, 03:38 PM
    Inspect the circuit board for evidence of moisture exposure. Look for oxide bridging of the printed circuit paths and/or burned spots. While the standing water may not have reached the unit, misting in the duct system may have occurred.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Mar 22, 2009, 04:45 PM

    So you can get the blower to run, but it won't run normally during heating cycle? And water was in the crawlspace. With this info, I would say you have a bad board, as KC suggested. I would check power to blower motor when it should be running(at approriate lead, heat, cool, fan, etc. Im betting on a bad board, but more info would help.

    It just so hard to trouble shoot this from here. I would hate for you to replace a board, or a motor, or anything for that matter, without being able to test it. Believe it or not, a visit from a repairman may actually save you money, vs replacing parts that may not be bad. Please let us know how things turn out. Good luck.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #6

    Mar 22, 2009, 07:25 PM

    By any chance does this furnace have a test terminal on the Circuit board. If so follow the instructions for testing the different compontents of the furnace.
    rainman5573's Avatar
    rainman5573 Posts: 6, Reputation: 1
    New Member
     
    #7

    Mar 22, 2009, 08:10 PM
    Quote Originally Posted by wmproop View Post
    rainman,,,its true (life is like a box of chocolates)
    does it (the led on circut board ) give a blinking code? if so on the inside of the door/panel you should find something to tell you what the code is

    you could also bypass the tstat bydisconnecting and jumpering the red and white tstat wires and see if you still have the problem
    WMPROOP, You are correct, and I failed to mention, there IS a blinking red light. The sequence is:
    1 blink followed by 3 blinks (or is it 3 then 1?), then repeats continuously, but there is no info found anywhere that tells what this blink code means and the error codes seem to be the hardest info to find on the web except for all of the jokes.
    The circuit board looks to be clean, free of dust AND corrosion. Maybe it is time to call for home service. I'm at a loss.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #8

    Mar 22, 2009, 08:50 PM
    Observe the blinks. The first digit will be short, the second digit long. Example: 1 short, pause, 3 long, pause/repeat = 13. 3 short, pause, 1 long, pause/repeat = 31.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #9

    Mar 23, 2009, 03:36 PM

    Kc, where would the diagnostic codes be found on this furnace? Or is it one of those that doesn't give the codes.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #10

    Mar 24, 2009, 03:54 AM
    A label titled "SERVICE" is usually found on one of the access panels, giving a description of the status LED and a list of the codes. Carrier, Bryant, and Payne use the same diagnostic format. The variable speed units can store fault codes for later retrieval, even if power has been interrupted.
    rainman5573's Avatar
    rainman5573 Posts: 6, Reputation: 1
    New Member
     
    #11

    Mar 27, 2009, 06:51 PM
    Quote Originally Posted by mygirlsdad77 View Post
    So you can get the blower to run, but it wont run normally during heating cycle? And water was in the crawlspace. With this info, i would say you have a bad board, as KC suggested. I would check power to blower motor when it should be running(at approriate lead,, heat, cool, fan, etc. Im betting on a bad board, but more info would help.

    It just so hard to trouble shoot this from here. I would hate for you to replace a board, or a motor, or anything for that matter, without being able to test it. Believe it or not, a visit from a repairman may actually save you money, vs replacing parts that may not be bad. Please let us know how things turn out. good luck.
    I'm not quite sure how to thank everyone at once, so I have responded by "quoting" several of you who attempted to help me.
    I DID finally call a local service man to the house, and thank goodness the "fix" was not any new parts for the furnace at all, just a $60 service call. The Bryant user's manual didn't list the blinking LED error codes and I missed seeing one of the re-set buttuons.
    All it took was re-setting the "manual-reset auxiliary limit switch" located on the blower housing. Easy to miss, as it is not readily seen behind the housing itself.
    Thank you to KC13, Mygirlsdad77, letmetellu and wmproop for your good advice!
    rainman5573's Avatar
    rainman5573 Posts: 6, Reputation: 1
    New Member
     
    #12

    Mar 27, 2009, 06:51 PM
    Quote Originally Posted by KC13 View Post
    A label titled "SERVICE" is usually found on one of the access panels, giving a description of the status LED and a list of the codes. Carrier, Bryant, and Payne use the same diagnostic format. The variable speed units can store fault codes for later retrieval, even if power has been interrupted.
    I'm not quite sure how to thank everyone at once, so I have responded by "quoting" several of you who attempted to help me.
    I DID finally call a local service man to the house, and thank goodness the "fix" was not any new parts for the furnace at all, just a $60 service call. The Bryant user's manual didn't list the blinking LED error codes and I missed seeing one of the re-set buttuons.
    All it took was re-setting the "manual-reset auxiliary limit switch" located on the blower housing. Easy to miss, as it is not readily seen behind the housing itself.
    Thank you to KC13, Mygirlsdad77, letmetellu and wmproop for your good advice!
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #13

    Mar 28, 2009, 09:23 AM
    Quote Originally Posted by rainman5573 View Post
    My Bryant gas furnace's, (model 376CAV downflow), blower will not come on.
    I removed the front doors and pushed re-set on the draft safeguard tube and the re-set for the manual limit switch. With the doors off, I can hold the blower door safety switch down and the blower comes on (does this mean the fuse is okay?) and the blower runs for a few minutes then turns off, then the burner comes on, but shuts off after a minute or two without the blower ever coming back on. With the doors replaced, the burner always comes on, but never does the blower. I have repeated this procedure several times with the same results. Is there something I can do to remedy the problem without the costly visit of a repairman?

    Short history: flooding caused several heat ducts to fill with water. The water never reached the height of the furnace base, but was within +18". The water has has now receded and is no longer in the crawl space of the house.
    In the past I have found two thing that can cause a furnace like yours to operate the way you describe, one is to have a dirty filter, the other is to have a evaporator coil for the A. C. partially stopped up therefore acting the same as a dirty filter would.

    If enough air does not go across the heat exchanger the burners will turn off from over heating, it will do this for a few times and then it will go into shutdown. When you open the bottom door of the furnace you break the power to the unit and this resets the shutdown, then it goes through the procedure all over again.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace ignites but blower won't start till furnace shuts down. [ 7 Answers ]

(Nordyne/Miller G3RA)-I have a furnace HSI(glow plug) that will ignite and burn until it gets too hot and shuts down. As soon as the furnace shuts down the blower starts to circulate air. The blower circulating air cools the furnace and it reignites.Shortly after the furnace ignites the blower...

Furnace blower [ 1 Answers ]

The blower to my furnace will turn on and blow cold air for like 30 seconds and then shut off and the furnace isn't running. When the furnace kicks on it runs fine.

Furnace blower [ 3 Answers ]

I have an intertherm central air/heat unit. The ac works fine. All of a sudden today the heater will come on but the fan won't blow. If I turn it on run the fan does, but on auto it doesn't. It still works fine when the ac unit is on.

Furnace blower doesn't come on [ 4 Answers ]

I have a Bryant furnace. The small draft inducer motor runs, but the blower doesn't come on. Any advice on this problem would be appreciated. Thank you.

Furnace blower fan [ 2 Answers ]

Call for heat on the furnace and the exhaust fan kicks in, the burners light, but the blower fan doesn't come on. What could be the problem?


View more questions Search