    Circuit Breaker Size
    I have a 48A 240VAC instantaneous water heater. What size circuit breaker do I need? I am thinking a 50A would do because it is not continuous.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Mar 11, 2009, 07:35 PM
    Read the mfg. data on the heater. It will tell you circuit size and protection. If it's not there, track down the information on the internet. How do you know it's 48 amp?
    ghoban's Avatar
    ghoban Posts: 4, Reputation: 1
    New Member
     
    #3

    Mar 12, 2009, 05:49 AM

    The tag on the heater says 47.8 Amps and the installation instructions recommend a #6 AWG wire. Its say to use appropriate size breaker.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #4

    Mar 12, 2009, 11:40 AM

    The reasoning in your first post is good. A 50 amp breaker is what you want.

    Slightly off topic, if this were a storage type water heater it would be considered a continuous load. In this case it is instantaneous so it is not considered continuous.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #5

    Mar 12, 2009, 08:46 PM
    I hate to ask, but why are you using an instantaneous water heater? They are real energy hogs and usually cost more to operate than tank type. Specifically the electric ones.
    ghoban's Avatar
    ghoban Posts: 4, Reputation: 1
    New Member
     
    #6

    Mar 13, 2009, 05:19 AM
    It's going in a cabin and won't be used much. I won't have to heat the water all week when we are not there.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Mar 13, 2009, 02:12 PM
    OK. I guess that is the one circumstance where it may be cost effective. Thanks for your response. An alternative would be a timer on a tank type, if you knew when you were going to be there. Good luck.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

What circuit breaker size should I use? [ 12 Answers ]

I recent purchased a heater that is rated 42.2 amps @ 240 volts. I was told by a licensed electrician that 8 awg would be fine for the heater. I have read some forums and now am questioning that also. I am wiring it in @ 220v So my questions are. Will it pull more amps @ 220v and if so how much?...

Circuit breaker size for several 300 watt flood light [ 10 Answers ]

I like to install 4 sets of flood lights. Each set is a pair of 150 watts bulb, for a total Of 300 watts per set, for a grand total of 1,200 watts for all 4 sets. Can I put all 4 sets of flood ligts on a 15A circuit? This is the way I like to install them: 2 sets of flood lights for the back...


View more questions Search