    Hydrotest for chilled water pipe
    Hello all,

    I want to know about the procedure of hydrotest conducted for chilled water piping?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Mar 11, 2009, 05:35 AM
    Quote Originally Posted by sattar123 View Post
    hello all,

    i want to know about the procedure of hydrotest conducted for chilled water piping?
    If you're asking about how we test water pipes after we install them we can do it in one of two ways.
    1) we pressure up a closed system and check the joints for air leaks ** or**
    2) We pressure the lines with water and check the joints for leaks that way.
    This works for hot, cold or chilled water. Good luck, Tom
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Mar 11, 2009, 05:43 AM
    From the book.


    1. Use ambient temperature water as the testing medium, except where there is a risk of damage due to freezing or if steel piping is exposed to air for more than one week before the water treatment is implemented.
    2. Subject piping system to a hydrostatic test pressure of 1.5 times the design pressure. The test pressure shall not exceed the maximum pressure for any vessel, pump, valve, or other component in the system under test. Check to verify that the stress due to pressure at the bottom of vertical runs does not exceed either 90% of specified minimum yield strength, or 1.7 times the "SE" value in Appendix A of ASME B31.9, Code For Pressure Piping, Building Services Piping.
    3. After the hydrostatic test pressure has been applied for at least two hours, examine piping, joints, and connections for leakage. Eliminate leaks by tightening, repairing, or replacing components as appropriate, and repeat hydrostatic test until there are no leaks and pressure holds for a period of two hours. Contractor for signature by Owner. Coordinate with Owner for witnessing the test and to complete a test report to be signed by the owner's representative.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Chilled water pipe [ 3 Answers ]

I am very new to askmehelpdesk.com. My question is, The building height is 300m. There are 6 chilled water risers going up to 125m height. The chilled water flow rate of each riser as follows. Riser 1 & 2 - 150l/s Riser 3 & 4 - 180l/s Riser 5 & 6 - 100l/s Chilled...

Chilled Water Volume [ 2 Answers ]

There are 4 Chilled each of the 461.8KW thermal cooling capacity in a chilled water circuit, I Need to calculate the to tal volume of chilled volume from equipment capacitiy and chemical quanitity required for chilled water system for energise the system, as well as monthly chemial and make-up...


View more questions Search