Honeywell RTH7400 seems to have locked my compressor
Woke in the middle of the night and started to adjust the temp. For some reason the thermostat seems to have locked the compressor so I can't get heat at all now! Read the manual three times, reset power to all units, still can't get the heater to kick on. Not a wiring issue because everything was working fine before... Replaced batts too just to be safe! Any help? I got 10 inches of snow and not much hope of getting out anytime soon!
|
|
|
 |
Ultra Member
|
|
Mar 2, 2009, 12:45 PM
|
|
|
Do you have backup/aux. furnace? Set the tstat to emergancy heat,maybe a little more expensive but is better than freezing till you get the heatpump fixed
|
|
|
 |
Ultra Member
|
|
Mar 2, 2009, 01:13 PM
|
|
|
If you have ten inches of snow on the ground I suspect that your heat pump should not have been running, there is a control in the heat pump that shuts it off after the temp drops below a certain point and the aux heat will kick in. Sounds like a problem with the aux heat. What do you have for aux heat, Electric or gas.
|
|
|
 |
New Member
|
|
Mar 2, 2009, 01:34 PM
|
|
|
 Originally Posted by letmetellu
If you have ten inches of snow on the ground I suspect that your heat pump should not have been running, there is a control in the heat pump that shuts it off after the temp drops below a certain point and the aux heat will kick in. Sounds like a problem with the aux heat. What do you have for aux heat, Electric or gas.?
Electric. But the Aux heat setting is lit on the thermo, but the condenser won't kick on.. I tried the fan "on" mode to see if I could get that to start and it wouldn't start either..
|
|
|
 |
New Member
|
|
Mar 2, 2009, 01:51 PM
|
|
|
 Originally Posted by wmproop
do you have backup/aux. furnace? set the tstat to emergancy heat,maybe a little more expensive but is better than freezing till you get the heatpump fixed
Tried this too.. but the condenser will not kick on in either mode..
|
|
|
 |
Ultra Member
|
|
Mar 2, 2009, 02:59 PM
|
|
|
Will the indoor fan run if the thermostat fan selector is switched to "ON"? If not, have you tried checking the power supply to the outdoor unit? If control power for the system is supplied by a transformer outdoors, any loss of power to the outdoor unit will bring the whole system down.
|
|
|
 |
New Member
|
|
Mar 2, 2009, 07:02 PM
|
|
|
No the fan will not run at all.. Plus the unit in the basement on the heat pump is humming, but the reset button will not stay in.. It keeps tripping out.. I suspect that the there is an issue with the outside unit like you said but that could be anywhere I guess.. But we are going to check it in the morning after we dig out! Thanks for your help!
|
|
|
 |
Ultra Member
|
|
Mar 3, 2009, 04:40 AM
|
|
|
Reset button? Like a low voltage circuit breaker? Set the thermostat selector to the emergency mode. If the system runs/heats, the problem is at the outdoor unit. I'm thinking... shorted contactor coil.
|
|
|
 |
New Member
|
|
Mar 3, 2009, 02:08 PM
|
|
|
 Originally Posted by KC13
Reset button? Like a low voltage circuit breaker? Set the thermostat selector to the emergency mode. If the system runs/heats, the problem is at the outdoor unit. I'm thinking...shorted contactor coil.
I tried the reset button on the unit downstairs, but when I throw the breakers on the unit, the reset button trips again..? So I still have nothing..
|
|
|
 |
Ultra Member
|
|
Mar 3, 2009, 08:31 PM
|
|
|
Try this: Disconnect 1 wire (any wire except "R") from the thermostat, and press reset button. If it trips, reconnect wire from previous step and disconnect another. Repeat this process until the reset doesn't trip; you've found the shorted circuit.
|
|
|
 |
New Member
|
|
Mar 4, 2009, 11:51 AM
|
|
|
 Originally Posted by KC13
Try this: Disconnect 1 wire (any wire except "R") from the thermostat, and press reset button. If it trips, reconnect wire from previous step and disconnect another. Repeat this process until the reset doesn't trip; you've found the shorted circuit.
Thanks so much, I will give it a try... Let you know how it turns up..
|
|
|
 |
Ultra Member
|
|
Mar 4, 2009, 04:21 PM
|
|
|
 Originally Posted by KC13
Try this: Disconnect 1 wire (any wire except "R") from the thermostat, and press reset button. If it trips, reconnect wire from previous step and disconnect another. Repeat this process until the reset doesn't trip; you've found the shorted circuit.
Somewhat trial-and-error, but will save you the costs of a multimeter AND fitness club fees... :p
|
|
|
 |
New Member
|
|
Mar 4, 2009, 05:34 PM
|
|
|
We found the problem. A bad interface board on the outside unit.. Looks like a mouse got to it.. Replaced it for $478 for parts and labor and I have heat..
|
|
|
 |
Uber Member
|
|
Mar 4, 2009, 09:23 PM
|
|
|
I have no idea why mice like circuit boards. They take out generators too.
|
|
|
 |
Ultra Member
|
|
Mar 5, 2009, 01:59 PM
|
|
|
Probably a baby looking for his "motherboard"... :p
|
|
|
| Question Tools |
Search this Question |
|
|
|
Add your answer here.
Check out some similar questions!
Trying to figure out honeywell rth7400
[ 8 Answers ]
Ok I have way too much info to confuse someone so here we go.
I have an old amana therm. Not sure which numbers are the model number so I'll list them all.
(Q674F 1022)
(T874C 1059)
class 2 30V max LR1620
here is how it was wired
brown---x2 out side went to 2 browns one to defrost board...
Honeywell RTH7400 Wiring
[ 5 Answers ]
I am replacing an old thermostat that had 6 wires. It had W,O,G,R,C,and Y. I reconnected all but the O. I can't find any help where this wire should go or if it should be connected at all.
Please advise. Thanks!
Honeywell RTH7400 wiring
[ 3 Answers ]
I am having problems with the installation of a Honeywell RTH7400 onto my existing system. I am connecting it to a Lennox HP26 (heat pump) with a Lennox Elite CB29M (blower coils).
The exterior unit wiring is as follows: orange to O, yellow to Y, white to W1, red to R, blue to C and no green.
...
Honeywell RTH7400 wiring
[ 2 Answers ]
I got a new honywell RTH7400. I need help wiring up the unit.
I just had a new Cold air central heating and A/C unit installed. It's electric heat and I need help with the wiring of the new honeywell RTH7400 5-1-1 control unit.
Wires:
Green
Yellow
White
Black
Red
Orange
View more questions