    Hi all,

    I have a York Stellar, model # P3CCD08N04501A I think it's a early 90's model. I have had an issue with it short cycling during heating, I have watched the sequence of events, here is what I see.
    1) Tstat calls for heat, usually it is very cold in the house due to no heating
    2) inducer runs
    3) HSI glows, about 35 sec
    4) 30 sec in, gas valve actuates
    5) flame on, stays on
    6) about 70 to 90 sec later blower fan comes on
    7) heat blows from registers for about 5 min, usually enough to raise temp in house by 1 or 2 degrees F
    8) gas valve shuts off
    9) HSI tries to reignite, gas valve will not actuate
    10) control attempts 2 more times then control led flashes continuously
    11) I turn power off and let it sit for at least 30 min, then try again, same sequence

    I had a service repairman come out and had tested the flame sensor and HSI. He said that they checked out fine. I removed the flame sensor and cleaned, same problem.
    The control P# White Rodgers 50E47-070
    fan limit P# L4064Y1433 Honeywell has an internal by metal heater, no adjustment for fan on, just fan off and high cutout set around 200F
    Gas valve P# 36E01 24VAC 1/2 X 1/2

    When I tested the voltage during the 3 attempts before control lockout, control never sent voltage to the gas valve, (even though HSI was on) I had voltage at the press switch and across the flame rollout switch, I had 24VAC at the control on terminal TH during the failed retries. Not sure what is happening, if I try to cycle the power to reset it won't work 3 attempt and fail, but if turn power off for at least 30 min it will refire with same results as list above.

    Thanks for any help you can provide
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Feb 22, 2009, 02:14 PM
    Based on the troubleshooting you have performed (not bad!) and the info you have given, it sounds very much like a faulty ignition module (fails to power gas control consistently). If I were performing this service call, executed the troubleshooting steps that you did, and observed the same actions that you did, I would replace the module.
    dport2009's Avatar
    dport2009 Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 27, 2009, 10:01 AM
    Quote Originally Posted by KC13 View Post
    Based on the troubleshooting you have performed (not bad!) and the info you have given, it sounds very much like a faulty ignition module (fails to power gas control consistently). If I were performing this service call, executed the troubleshooting steps that you did, and observed the same actions that you did, I would replace the module.
    Thanks for answering my question so quickly.
    I had ordered the control module P# IGM 50E47A, I installed it yesterday and everything is working normal now, Thanks for your help.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Feb 27, 2009, 04:41 PM
    Your success is my reward. I just love (sniff) happy endings... :)
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Feb 27, 2009, 05:46 PM

    I need your crystal ball KC. I was thinking pressure switch, when they said they had 24v across it and the flame rollout, when there should be no voltage across it. Guess they were testing to a ground, in and out. Threw me off.

    Deport, I wish every one that asked a question here were as informative as you. Great job. And the best part is, you already had the part on order, knowing that most likely this was the problem. I see you are a new member, hope you stick around and use the sight. Maybe you could help some other folks out.
    dport2009's Avatar
    dport2009 Posts: 3, Reputation: 1
    New Member
     
    #6

    Feb 27, 2009, 11:28 PM
    Quote Originally Posted by mygirlsdad77 View Post
    I need your crystal ball KC. I was thinking pressure switch, when they said they had 24v across it and the flame rollout, when there should be no voltage across it. Guess they were testing to a ground, in and out. Threw me off.

    deport, i wish every one that asked a question here were as informative as you. Great job. And the best part is, you already had the part on order, knowing that most likely this was the problem. I see you are a new member, hope you stick around and use the sight. Maybe you could help some other folks out.

    Thank you, I appreciate the welcome
    I was testing to ground for the 24 vac, I knew by looking at the schematic that the components in the circuit have to be satisfied in order for there to be voltage at the control module i.e. press switch, flame rollout, ls1, ls2. While its trying to run. So I sat down in front of this thing for about 4 hours till I was just sick of it. LOL
    I didn't order the module till I read KC's reply, got it second day air. You know I just stumbled across this forum and I couldent beleve how informative and how quick the response were, very nice forum. I hope to become a reguler here and help out where I can
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #7

    Feb 28, 2009, 07:47 AM
    I'll give you my endorsement for the up-and-coming member of the week award. You made our part easy, I'm guessing that you took the time to read some other threads and figured out how to help us help you. Good job. P.S. to MGD77 The crystal ball is on the fritz, but I got some good help on one of the other repair advice forums and the parts are ordered.;)
    cvle99's Avatar
    cvle99 Posts: 1, Reputation: 1
    New Member
     
    #8

    Dec 14, 2009, 04:48 PM

    Hi,

    I am new here, I have same problem here but after I replace igniton module it still have same problem, can anyone help me please.

    Thanks
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #9

    Dec 15, 2009, 04:20 AM

    Have you checked the status light on the circuit board for activity? Look for a label with codes & instructions on the front/blower panel.
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

York Stellar Gas furnace issue [ 7 Answers ]

Hi have a York Stellar furnace and its about 15 years old, it was working fine suddenly it wouldn't lite up, seems like the motor is working fine but the piece that's lits up for the igniter does not lit up. Furnace is not blowing any air, no flames going on. Please help its cold out here.. ...

York Stellar Furnace Heating up Furnace Room to 110 Degress? [ 2 Answers ]

I have a York Stellar Furnace in my newly purchased house. Furnace is 15 years old. Furnace is releasing hot air from front grills and heats up furnace room to 110 Degrees. I had a Bryant Furnace in another house and this never happened. All plenams and ducts are taped and sealed so the heat is...

York Stellar LP furnace cycles quickly [ 1 Answers ]

After exhaust fan operates for 20 sec, ignitor glows for 15-20 sec, then gas comes on for 1 sec. then goes out instantly, ignitor stays on and gas ignites in another 20 sec. This cycle continues without interruption. Consequently, heat never comes on.

York Stellar Gas Furnace cycles quickly [ 4 Answers ]

Our LP gas furnace seems to be cycling rather quickly. The exhaust blower will come on for a few seconds, then the burner ignites properly. When the main blower fan kicks in the burner shuts off immediately. The blower continues to run for 30 sec. then stops. The exhaust blower continues for 45...

York Stellar gas furnace issue [ 1 Answers ]

My ten year old York gas furnace will run fine but intermittently it will not start back up again when the temperature drops. I replaced the thermostat to a Honeywell seven day programmable. That did not fix the problem. If I turn off the furnace at the furnace, wait about ten seconds, and turn it...