Fan blows but no cold air!
Believe it or not in Houston today we got up to 85 degrees!! We have a Train XE 1100. I turned the thermostat on to cool. AC Kicked in... we have fan blowing air through the house, but no cold air.
Outside at the unit the top fan is turning... but the hose that sends the cold air into the house it not cold at all??
I have a mulitmeter and I am just maybe handy enough to fix it. Ideas?:confused:
Thanks,
Buster
|
|
 |
Ultra Member
|
|
Feb 18, 2009, 04:47 PM
|
|
OK,, take that multi meter and see if the compressor is running,, but if you can`t you should be able to turn off power to a/c and while standing very close with your ear even closer have someone to turn it back on,, besides hearing the fan come on you should be able to hear the compressor come on also,, if not you could take the wire off the contactor that goes to the fan so it won`t come on,then turn power back on again and hear the compressor only come on,,
,let us know
|
|
 |
New Member
|
|
Feb 19, 2009, 03:27 PM
|
|
Ok, so I disconnected the fan, and turned on the AC. I could hear a click sound and then a humming/buzz sound. But the buzzing was very quiet.
There was also a flashing red led on the circuit board.
Thanks,
Buster
|
|
 |
Ultra Member
|
|
Feb 19, 2009, 03:30 PM
|
|
Does the capacitor appear swollen/distorted on the terminal end (like a frozen carbonated beverage can), and/or is fluid leaking from it? If so, replace (disconnect power supply!).
|
|
 |
Ultra Member
|
|
Feb 19, 2009, 07:39 PM
|
|
Turn the power off going to the system remove the electrical cap on the compressor to see if one of the three wires are burnt off. I agree with KC13 check the capacitor first.
|
|
 |
Ultra Member
|
|
Feb 20, 2009, 05:01 PM
|
|
If wire to the compressor is burned,, its not likely that the compressor would be humming or buzzing,, unless you are hearing the contactor humming
|
|
 |
Ultra Member
|
|
Feb 20, 2009, 07:56 PM
|
|
I agree the compressor won't hum or buzz with a leg of power missing but you have to start some where. I assumed he or she was hearing the hum (sound) of the contactor or reversing valve with out the compressor running.
|
|
 |
New Member
|
|
Jul 16, 2009, 02:17 PM
|
|
Thank you gentlemen! Sorry for the slow reply. It was the capacitor. I replaced it and now we are good to go...
Again thanks for the tips.
Buster
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Furnace Blows Out Cold Air
[ 1 Answers ]
I own a duplex and my tenants upstairs claim the furnace is blowing out cold air. :eek: I had the thermostat replaced and they said it helped but it still blows out cold air at times. I asked them if they had the heat up high and the furnace needs to cool down and they said no. I'm wondering if...
Heater blows hot air, then cold
[ 1 Answers ]
My home heater comes on, blows hot air for 10 to 15 minutes, then cold air until we turn it off. If we leave it off for about 30 minutes, it blows hot air again, for 10 to 15 minutes, then cold again. What do you think is the cause?
Furnace blows hot air for 3 min. Then cold for 3 ?
[ 4 Answers ]
Furnace blows hot air for about 3-4 min. (burners all firing nicely) then burners go out but air continues to blow (cold) for 3-4 min. All registers are open and the pressure is VERY strong (small house - 6 ports) cycle repeats about every 10 min. or so. Also, what would the black plastic bucket...
Furnace blows cold air
[ 3 Answers ]
Yesterday my furnace stopped heating my home. It is 3 years old & I did some minor troubleshooting. The filter is not clogged and the blower is circulating air normally. I checked inside the unit & the ignitor coil is heating and starting the gas jets burning, but they shut off after about 10...
View more questions
Search
|