Feb 8, 2009, 04:40 PM
|
|
HUMIDIFIER does not shut off
I have a Carrier 58 SX furnace (22 years old) and had a Carrier Bypass Humidifier installed several years ago (HUMCCLBP 18-A). The humidifer water is now running all the time and does not shut off when the furnace does. The humidistat is wired to R and C at the furnace which I assume or 24 V connections. The panel reading left to right at the furnace has Y W H R GH C and G terminals. Any help you can provide would be greatly appreciaed.
Thanks,
Bob
|
|
 |
Ultra Member
|
|
Feb 8, 2009, 04:43 PM
|
|
It should be wired to "H" and "C" at the circuit board. This assures the humidifier circuit is only powered during heating cycles. How did it end up connected to "R" and "C"?
|
|
 |
New Member
|
|
Feb 8, 2009, 04:56 PM
|
|
Thanks for the very quick answer. It has always been wired this way and it worked for a few years. I assume the humidistat is controlling the water solenoid some how? The humidistat does work when I manually turn it up or down although the water does not shut off until I turn in below the humidity threshold.
Thanks,
Bob
|
|
 |
Ultra Member
|
|
Feb 8, 2009, 05:01 PM
|
|
There must be another control somewhere, perhaps an airflow switch or current-sensing relay. Otherwise, the humidifier would run water anytime the humidistat was set above the indoor humidity, with or without the system running. Using the "H" terminal will assure it only runs during a heating cycle.;)
|
|
 |
New Member
|
|
Feb 8, 2009, 05:06 PM
|
|
Thanks I will give it a try after checking the H & C are a 24 V supply. I am not aware of any other sensors unless it is in the humidistat itself but who knows? It is a Carrier humidistat also and the entire unit was installed by the dealer so I am wondering why the would hook it up to R & C versus H & C? Again, thanks for your help!
Bob
|
|
 |
Ultra Member
|
|
Feb 8, 2009, 05:09 PM
|
|
You're most welcome. You will find that the "H" terminal is only powered when the gas control is, or in some cases only when the blower is. The "H" designation is for humidifier.
|
|
 |
New Member
|
|
Feb 8, 2009, 05:21 PM
|
|
Now that I think of it, I do not believe it has run correct since the last time it was serviced. I wonder if the tech had to remove those wires for some reason and put them back in the wrong locations?
|
|
 |
Ultra Member
|
|
Feb 8, 2009, 05:23 PM
|
|
Could be. While an error on his part (if so), at least it suggests he was actually doing something beyond a "dog 'n' pony show".:rolleyes:
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Do I need a humidifier and if so, what kind?
[ 1 Answers ]
My apartment has hot water baseboard heat that is controlled by a zone valve connected to a t-stat. The exterior walls of the apartment are poorly insulated. On the really cold and windy nights we have to keep the heat up all the way to battle the outside temps. We all wake up with sore throats...
Whole Home Humidifier
[ 1 Answers ]
I am looking at installing a whole home humidifier on to my furnace system which is currently a dual fuel system with a heat pump and a high efficiency gas furnace. I am a do it yourselfer and I plan on doing the install myself. I have looked at the Aprilaire 600 bypass model and I think it may...
Humidifier causes flood?
[ 2 Answers ]
Last night I turned the humidifier on for the first time on my new heating system (an entire new gas furnace and air conditioner was installed this summer and this is the first time I needed the humidifier).
To do this, I simply turned the knob mounted on the return duct on my unit to about...
Humidifier Power
[ 1 Answers ]
I have recently installed a whole home humidifier that runs on 24 VAC. I currently am running it off a power brick plugged into a standard 120VAC outlet. I would like to set up the humidifier such that it only runs when the blower is running. I have put a meter across the C and G terminals where...
Aprilaire Humidifier
[ 1 Answers ]
I just installed an Aprilaire 550 humidifier on my Goodman furnace but can't figure out how to wire it. The furnace has a control board which has a 24 volt HUM terminal. My humistat has two terminals. I am looking for a very simple explanation on how to wire this thing up.
View more questions
Search
|