Whirpool Electric Range/oven causes circuit breaker to trip
I have a 3 year old Whirlpool electric slide in range that has started to cause the circuit breaker to trip. Strangely, it occurs when both the range and oven are on, and we open/close the oven door. It is the only appliance attached to this circuit breaker. I did have to replace the computer board on the range approximately 6-9 months ago. When it was replaced (it had an error message that required its replacement) it has worked fine till now.
This has been going on for the last two weeks. Today the circuit breaker will no longer stay on with the range plugged in. It will remain on if its not.
Help! :)
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 7, 2009, 06:55 PM
|
|
Circuit breaker probably worn out from resetting too much. You will have to take the unit apart to find the short circuit. Sometime a wire will burn off a heat element especially a bake or broil element in the oven. The only way to find the problem is to look for it. I wish I had a easier solution.
|
|
 |
New Member
|
|
Feb 8, 2009, 07:28 AM
|
|
I actually pulled the range out and unplugged it. It didn't take long to find the problem. I unscrewed the metal box where the power cord connects to the range. One of the lines (red) is discolored - black, and the screw that holds it to the "block terminal" is melted. The nut actually melted onto the metal box cover, but I was able to pull it apart. I was thinking of buying a new block terminal, and power cord. Could the short be in the cord? Thanks for your response - you were right on target.
Also, should my circuit breaker still be OK... or likely be OK? My house is only 3 years old.
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 8, 2009, 07:53 AM
|
|
Usually the cord is not shorted. The connection was left a bit loose when installed and that caused a HOT spot for the heat to concentrate on. You can test the cord if you wish with a OHM meter.
|
|
 |
New Member
|
|
Feb 8, 2009, 09:46 AM
|
|
Model # GY398LXPS00
I've looked up the parts on Sears Parts Direct.
So... your thought is that the block terminal being replaced, and properly secured - looks like a god bet on fixing?
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 8, 2009, 10:38 AM
|
|
If you see the burn spot on the metal cover that is where the wire shorted to. The red terminal has meltdown for sure. If you can afford a new cord do so if not get a replacement end terminal and crimp on a new one. If you do not have a crimp tool it might be better just to replace the cord and block at the same time. Make sure all wiring is tight but do not brake the new terminal block. Use the correct tools not a pliers to tighten the nuts with.
|
|
 |
New Member
|
|
Feb 14, 2009, 08:20 AM
|
|
Just a little follow up. Replaced the block terminal, and replaced the power cord. All is working again - no circuit breaker tripping!
Thanks - you were a huge help.
|
|
 |
Heating & Air Conditioning Expert
|
|
Feb 14, 2009, 08:25 AM
|
|
Good deal. Glad you got it going.
|
|
 |
New Member
|
|
Apr 15, 2012, 09:52 AM
|
|
Hi Hvac1000 & Siep68,
Thanks so much for your posts. Our stove tripped the breaker today and would not reset. After finding your post we decided to check the connections. Upon inspection we had almost the same issue as you. The loose connection of the red wire was the Factory installation and not the electrician installation. This loose connection caused the same problem.
I will try to upload a picture of our problem.
Thanks again,
Connie & Tony
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Furnace sometimes won't start, then need to trip circuit breaker on and off
[ 5 Answers ]
I live in a condo, and I started experiencing this problem in the middle of last winter.
I will notice that the temperature will drop past when the furnace should kick in. I found that tripping the circuit breaker on and off will usually do the trick. It would happen intermittently. It could...
How Double Pole Circuit Breaker Trip?
[ 9 Answers ]
On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? Also, I recently bought a new electric range. I...
Circuit Breaker didn't Trip
[ 7 Answers ]
I have a 1 year old home. The bathroom outlet is a GFCI outlet on a circuit protected by a 15 amp ARC FAULT BREAKER. Today my wife plugged her hair blowdryer and the base of the cord lit up like an arc welder. This lasted for 5-8 seconds before the cord completely melted and the fireworks...
Circuit breaker failed to trip
[ 2 Answers ]
I made a big error today on wiring a new circuit. I pulled 2 cables (for 2 circuits) back to the consumer panel and then connected the wrong cable. The cable that I connected was stripped at the other end but not yet connected to anything. When I went to inspect it, I tugged on it and there was one...
View more questions
Search
|